I have to make a ladder logic for a pumping station for 4 pumps, 3 duty and 1 standby, How can I change the duty of a pump if it is running for a long time?

three pumps are interlocked to level measurement from a level transmitter, if 20% level than 1st pump starts, if 45% level then 2nd pump will start and if level of tank is 75% than 3rd pump will start and for level is 90% ,4th pump will also start...
But if for a long time level is 25-40% than only pump 1 will have to run continuously, that could increase its worn...I want to change duty in such case.

experts kindly help,
It will be a great favour from your side.
Thanks in advance
 
As mentioned, it's been covered before. .. Again this week actually.

I see this concept of even wear coming up often, but I sometimes wonder why people want to do it. Do you really want all your pumps to be worn the same amount? So when one falls over, the other 3 are not far behind...

Personally I prefer a 75% / 25% duty ratio. Wear one machine out at a time.

But if you really want to swap duties if a pump is running for a long time, then just time / count the minutes it's been running for. When it has run for more than your time Setpoint, then do a duty change.easy.
 

Similar Topics

Hello I have up to 8 pumps that, depending on demand, I'll run however many I see fit. Pressure is my setpoint and a pid and 8 inverters deal with...
Replies
13
Views
3,273
Dear all, I am doing a PLC program for 2 duty and 1 standby pump rotation control by using Mitsubishi Q series PLC. The control sequence of the...
Replies
11
Views
10,105
Guys, I am doing a pump station with 4 pumps, duty selectable, rotating etc etc etc. and the combinations are huge. Some of you guys would have...
Replies
5
Views
3,248
Hello Friends, I am looking for a way to take my PID Output( it is the result of my PI Algorithm in Real format) and generate a PWM Signal in...
Replies
16
Views
2,477
Just want to make sure my thought process is correct before I proceed. I have a linear actuator with a 3min / 17min duty cycle (3 on, 17 off) I...
Replies
2
Views
1,128
Back
Top Bottom