Issues with delta HMI

rejoe.koshy

Member
Join Date
Dec 2011
Location
kolkata
Posts
195
HI,
I have a delta make HMI (cat no- DOP-B05S101)which is hooked to Siemens s7-200 Plc.Due to some issues with the screen of the HMI, I replaced it with a new HMI (cat no- DOP-B05S111) & then downloaded the program.

For unknown reasons , I am getting a communication 3 error on the HMI.I have checked the configuration parametes several times & found them to be matching with the old one.I am at my wits' end.


Pls help!!
 
If the communication settings weren't changed, then it should be a problem in the wiring or on the PLC end.

But the wiring wasnt changed & the old model was working fine with existing wiring.The communication protocol is RS485.Will the wiring be different for different models of HMI??
 
I thought all of the "B" series screens were the same in terms of communications.

They do have some communication notes regarding the S7 in their DOP Communication (page 205) documentation - a suggested delay of 10 to 30. Maybe it's firmware related?
 
I thought all of the "B" series screens were the same in terms of communications.

They do have some communication notes regarding the S7 in their DOP Communication (page 205) documentation - a suggested delay of 10 to 30. Maybe it's firmware related?


Thanks- BlueAltezza for the guidance.Can you please direct me to the link for communication manual....would like to go through it in detail.
 
The serial port might be locked up on the PLC. Did you power cycle it? Do you still have the old screen to retest?

Yep, the old screen works fine.All parameters in the new & old are identical except the communication delay settings.

Could the communication delay be the issue??
 

Similar Topics

Guys, I just started a new job at a company in Charlotte NC that has been here for many years. The transformer feeding part of the plant is an old...
Replies
15
Views
6,491
Hi all, this a good community to join with, I would like to know how to make connection between DELTA PLC with Model: DVP-12SA2 to VFD DELTA S1...
Replies
0
Views
3,353
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
0
Views
60
Hello everyone, I've had this issue for the last 2 days where I try to assign the profisafe address to an IO block (6ES7 146-6FF00-0AB0) but when...
Replies
5
Views
156
I'm at a loss here and hoping someone else has seen this: Background: We've got two identical machines on our floor (we'll call them machine A &...
Replies
0
Views
70
Back
Top Bottom