Rslinx Classic 3.9 Does not Show DDE/OPC tags

Mray

Member
Join Date
Mar 2018
Location
Toronto
Posts
90
Hi,
I am gonna use Rslinx classic 3.9 to copy DDE/OPC tags' link from CompactLogix CPU to Excel through Ethernet/IP but It does not show any of them in Copy DDE/OPC link window. The window is empty with the title of:

RSLinx OPC Server (Node:<Local>)\MyPLC\Online

I have configured DDE/OPC as:
Station (decimal): 49
Remote: Remote ControlNet
 
When you set up your OPC topic in RSlinx, did you browse to the controller? Sometimes folks select the comm card instead of the CPU, something to check.


Yes I chose the CPU. I just right click on CPU and choose Configure New DDE/OPC
 
Have you ever tried opc with this version of rslnix,
You need rslinx gateway for OPC to work.
Check in help menu does it show rslinx gateway
 
Have you ever tried opc with this version of rslnix,
You need rslinx gateway for OPC to work.
Check in help menu does it show rslinx gateway



Rslinx.jpg
https://ibb.co/ygQ0mC9
 
Last edited:

Similar Topics

Hi, I am working on a project, where I face a issue with respected to Network Dropout. The PLC is connected to a 16 port unmanaged switch, where...
Replies
7
Views
155
Hey All, I am sorry to ask this, but i still gotta do it. What happens if I close RS linx? Will it cause network interruption and PLCs will lose...
Replies
5
Views
147
Does anyone know if there is a way to import RSLinx Classic data into FT Linx? We have a quite extensive configuration set up, and it would be...
Replies
8
Views
2,524
Hello, I entered my controller IP address as 192.168.1.100 (Local) for 1769-L33ER. It worked fine until couple month and found the controller kept...
Replies
1
Views
1,129
Hi All, Looking for some clarity regards the relatively recent rebranding of RSLinx Classic. From what I can make out from the RA website and...
Replies
9
Views
2,357
Back
Top Bottom