Siemens S7 - 400 - Profinet Device name reset/assign automatically
chapani
Jul 2014
Tax heaven
22
Dear all,
Im having troubles finding a solution with Siemens Step 7 V5.5 and CPU CPU 416-3 DP + CP 443-1 for Profinet IO. Profinet IO devices are MOOG Servo valves. So I prepared the HW configuration with scalance switch X216 and on one port of the switch connected two valves in series, on another port of switch connected other two valves. Profinet device names were assigned to each valve from Hw config edit Ethernet node -> Assign device name. added topology with partner ports properly and everything downloaded to PLC and is working fine. If I change two Ethernet cables from Port 1 to Port 2 and vice versa of scalance going toward the valves it will detect a mismatch and need to be done factory reset from HW config for each single valve and then again need to assign profinet device name properly and everything working well. The thing is that I would like to do this automatically, and I don’t find a way in PLC program by using some SFC or SFB or similar to be able to reset device node name, so I can assign new name to the device from PLC, or from Wincc via PLC. Is there any hint to doing that or is not possible at all with S7 – 400 CPU. I find it strange because same thing with allen Bradley and Ethernet IP, or Beckhoff and ethercat can be done very easily.
Thank you
If you switch ports so that the topology do noit match, then yes the Profinet system fails. It is supposed to.
If you want to swap ports freely, then do not use topology.
Hi Jasper,
maybe I didnt explain my self good enough. Topology fails, but test is intended due to acutual application of valves, that should be intalled on the machine, lets simplify, machine has two modules, on each module are 2 valves. and there is a possibility to exchange the modules, so module number 1 can be placed on position of module number 2 and should behave and software for controlling will be of module number 2 in that moment, and vice versa for other module. Port 1 scalance cable is going always to physical position of module 1, and port 2 two physical position of module 2. If I do not save topology than by interchanging cables, (simulating exchange of position of modules) will not work, because module 1 will always be module 1, it doesn't matter where it is, but I want to avoid this, I need to get somehow reset and assign new profinet device name automatically or semi auto from PLC sw.
is that possible with S7 400 CPU? if not than I need to switch to Beckhoff or similar
Hi, I am trying to setup a S7-400 with PI and PO memory. This memory is associated with profinet devices according to my research. I don't have...
4,233
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
322
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
632
Good Afternoon. I am having a problem going online with S7-400. Attached is the error that I am getting. I have looked at the help file but the...
1,764
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
1,499