Control Logix Processor Redundancy in the Same Rack

vel_sathish

Member
Join Date
Feb 2007
Location
Tamilnadu
Posts
15
Hi,
Wish U Happy New Year !

In one of my project I have Two Control Logix Processors in the same Rack connected to an HMI (PV 1500 Plus) through Controlnet. I cant able to acheive the Redundancy between the processors. Can anyony help me to configure the redundancy part in the processors?


Regards,
S.Sathish
 
Redundancy for ControlLogix has a set hardware setup - two identical racks with identical modules.


The User Manual is 1756-UM523D-EN-P.
 