Subnet Mask problem

Hi all,

We have to change the subnet mask on ~400 E/IP devices to make the network bigger. Is there a quick way to do that? I can do them one at a time, but that will take a couple days. Is there a program or script that could do that.

Alternately, if we just change the subnet mask on the PLC and switches (/22), but leave the subnet mask on the IO blocks and VFDs at /24, will that work? The IO blocks and VFDs are only communicating with the PLC, not any of the devices on the larger subnet.

Thanks in advance for your help.
  Reply With Quote
Old October 18th, 2018, 12:16 AM   #2
Geoff White
Member
Australia

Geoff White is offline
 
Join Date: Oct 2005
Location: Brisbane
Posts: 275
The existing devices wont be able to talk to any address outside of the existing subnet. If they don't need to it wont be a problem.

It is worth updating the PLCs and HMI so that they can be connected to from the new address space.
  Reply With Quote
Old October 18th, 2018, 05:47 AM   #3
robertkjonesjr
Member
United States

robertkjonesjr is offline
 
Join Date: Jan 2009
Location: NH
Posts: 502
Are you going in the wrong direction? That's a lot of devices on a subnet, and now adding more, leads to more risk.

Maybe smaller subnets with a router / firewall in between to control traffic flow - provides for better security from segmentation and reduced risk of harm from other devices in the network.

If you have that many devices, I would expect a fully managed infrastructure so little might be required besides a new architecture design and some configuration. Especially if you already have to go through the work of updating all of those devices, additional changes might only be incremental.
  Reply With Quote
Old October 18th, 2018, 07:14 AM   #4
Saffa
Member
New Zealand

Saffa is offline
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 916
I'm curious to know how you have 400 odd devices on a /24 subnet when the maximum number of hosts is 254. Or are there two subnets and you are essentially looking at combining them into one by changing to /22, giving you 1023 hosts?

As robertkjonesjr says, using a router may be a better option. Set the gateway address in the PLC to be that of the router's interface which is facing your /24 network. Any traffic that needs to transition to other networks will be sent to the router.

If you don't need to talk to your drives etc from your /22 network then no need to change. But if you do then you would need to set their default gateways accordingly to that of the router.
  Reply With Quote
Old October 18th, 2018, 11:23 AM   #5
Jeebs
Member
Belgium

Jeebs is offline
 
Join Date: Feb 2007
Location: Leuven
Posts: 1,037
Do all of these devices need to be connected to each other? I feel it could become quite dangerous quite fast.

Common way of this is having machine specific devices on a local separate network. With the PLC having a secondary network card to communicate with the plant. With Rockwell this setup still allows you to see all the devices, but it makes it waaaaaaaaaaaaaaaaaaaay harder to make a simple typing error and potentially breaking a machine. Or a person.
  Reply With Quote
Old October 18th, 2018, 01:58 PM   #6
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,935
Quote:
Originally Posted by Saffa View Post
I'm curious to know how you have 400 odd devices on a /24 subnet when the maximum number of hosts is 254. Or are there two subnets and you are essentially looking at combining them into one by changing to /22, giving you 1023 hosts?

As robertkjonesjr says, using a router may be a better option. Set the gateway address in the PLC to be that of the router's interface which is facing your /24 network. Any traffic that needs to transition to other networks will be sent to the router.

If you don't need to talk to your drives etc from your /22 network then no need to change. But if you do then you would need to set their default gateways accordingly to that of the router.
Everything he said. Also, if you do what you intend (only change subnet for some of the devices) it will work, but it is throwing a ton of best practices out the door, and it will be very easy to accidentally screw things up down the road.
  Reply With Quote
Old October 18th, 2018, 11:12 PM   #7
shawn_75
Member
United States

shawn_75 is offline
 
Join Date: Apr 2010
Location: KY
Posts: 344
If these devices are getting their IP via DHCP, then just update the DHCP server to serve the new subnet mask.

Be careful with having your devices on different subnets in the same address space. The subnet mask, along with the IP address, determines the broadcast address the device listens to. While normal IP traffic may work just fine, things like discovery type protocols won't work.
  Reply With Quote
Old October 19th, 2018, 09:26 PM   #8
mk42
Member
United States

mk42 is offline
 
Join Date: Jun 2013
Location: MI
Posts: 1,935
Quote:
Originally Posted by shawn_75 View Post
The subnet mask, along with the IP address, determines the broadcast address the device listens to. While normal IP traffic may work just fine, things like discovery type protocols won't work.
This is a really interesting point. Most of the protocols I work with are layer 2, I forget that layer 3 protocols are just as common.

Things like DHCP and BOOTP require IP (layer 3) broadcasts.
  Reply With Quote
Old October 19th, 2018, 10:14 PM   #9
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Tennessee
Posts: 2,238
Before you start !!!
consider this, you also need to consider all messaging, hmi, scada, SQL, odbc, and other potential interface issues.

think this out and look at all programs first, make a plan, and then implement.
as you said, 400 is a lot.

better to take your time and look at everything than to shut down production and ask what happened.

james
  Reply With Quote
Old October 20th, 2018, 09:29 AM   #10
damica1
Member
United States

damica1 is offline
 
Join Date: Aug 2015
Location: Illinois
Posts: 565
Here's a list of how you might setup up your subnets.


Addresses Hosts Netmask Amount of a Class C
/30 4 2 255.255.255.252 1/64
/29 8 6 255.255.255.248 1/32
/28 16 14 255.255.255.240 1/16
/27 32 30 255.255.255.224 1/8
/26 64 62 255.255.255.192 1/4
/25 128 126 255.255.255.128 1/2
/24 256 254 255.255.255.0 1
/23 512 510 255.255.254.0 2
/22 1024 1022 255.255.252.0 4
/21 2048 2046 255.255.248.0 8
/20 4096 4094 255.255.240.0 16
/19 8192 8190 255.255.224.0 32
/18 16384 16382 255.255.192.0 64
/17 32768 32766 255.255.128.0 128
/16 65536 65534 255.255.0.0 256
__________________
David M. Camp

Marshall Electric / https://mei-tech.com/monitor-and-control

Please Download from our download section "Monitor and Control" .pdf.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
IP subnet mask lesson ? Jeff23spl LIVE PLC Questions And Answers 8 May 13th, 2014 12:53 PM
Simatic H System Problem after download ry_fern LIVE PLC Questions And Answers 0 March 10th, 2013 07:01 AM
Ethernet Subnet Mask Phrog30 LIVE PLC Questions And Answers 18 September 15th, 2012 08:19 PM
TI-565 Weird comms and/or config problem RoTaTech LIVE PLC Questions And Answers 7 May 4th, 2009 06:59 PM
Ab Plc5 Rio Problem. fernandes LIVE PLC Questions And Answers 5 March 7th, 2004 02:25 PM


All times are GMT -5. The time now is 10:30 AM.


.