I am fairly new to programming so this will be something to build on. I am familiar with intergers and what they do but Ive mostly just been programming ladder logic. From a quick good search it does seem to make navigating easier but there seems to be a learning curve.
  Reply With Quote
Old October 19th, 2018, 08:58 AM   #17
PLC Pie Guy
Member
Canada

PLC Pie Guy is offline
 
PLC Pie Guy's Avatar
 
Join Date: Jun 2013
Location: Halifax
Posts: 705
[quote=TheDude_Abides;794897]Currently the Estop is wired in series with the line voltage for the PLC. However, now that I think about it it may be better practice to have the Estop reset the cylinders in case of a pinch injury.

I would have a real problem with this one!!!

Sounds like this machine is a death trap! The E-Stop should be wired to a safety circuit. Not the PLC line voltage, that is ridiculous.
  Reply With Quote
Old October 19th, 2018, 09:11 AM   #18
sparkie
Lifetime Supporting Member
United States

sparkie is online now
 
Join Date: Nov 2014
Location: KS
Posts: 811
Man, I would like to know what integrator did this work.
  Reply With Quote
Old October 19th, 2018, 10:56 AM   #19
TheDude_Abides
Member
United States

TheDude_Abides is offline
 
Join Date: Sep 2018
Location: Chattanooga
Posts: 44
Guys, with all do respect. Im not asking for judgment to be passed let alone criticism. I've recently taken over the electrician job and I only have so many hands. alot of equipment here is lacking plenty of safety equipment. I am trying to implement as much as I can in a little amount of time. there are so many hours in the day.
  Reply With Quote
Old October 19th, 2018, 11:00 AM   #20
TheDude_Abides
Member
United States

TheDude_Abides is offline
 
Join Date: Sep 2018
Location: Chattanooga
Posts: 44
With that being said, would anyone mind taking a look at the program I just rewrote for this and let me know if you see any discrepancies? If not, its totally understandable. I'm trying to learn through this whole process and any helpful advice from experienced personnel would be genuinely valued.
Attached Files
File Type: zip LSC BIG BLUE BENDER - REWRITE.zip (10.9 KB, 3 views)
  Reply With Quote
Old October 19th, 2018, 11:03 AM   #21
TheDude_Abides
Member
United States

TheDude_Abides is offline
 
Join Date: Sep 2018
Location: Chattanooga
Posts: 44
[quote=PLC Pie Guy;794926]
Quote:
Originally Posted by TheDude_Abides View Post
Currently the Estop is wired in series with the line voltage for the PLC. However, now that I think about it it may be better practice to have the Estop reset the cylinders in case of a pinch injury.

I would have a real problem with this one!!!

Sounds like this machine is a death trap! The E-Stop should be wired to a safety circuit. Not the PLC line voltage, that is ridiculous.
This is a very old plant with the last electrician having been a dinosaur with very old school line of thinking. Ive been in several cabinets, namely a natural gas furnace where the safety relay was completely unwired and a bundle of wire nuts on all the wires from said safety relay nestled underneath it in the wireway. Needless to say the furnace was shutdown immediately.
  Reply With Quote
Old October 19th, 2018, 11:47 AM   #22
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,263
That's very good work, simplifying the original programmer's mess of latches.

Abstracting the digital inputs into their own subroutine is a very good practice. It also gives you a place to add "debounce" timers if short or inadvertent triggers of a sensor are a problem.

The two sensors I would add a delay timer (maybe 50 to 100 ms) to are the Foot Switch and the Setup/Auto selector. Just use the input point to run a TON timer, and use the /DN bit of the timer to run your internal sensor status bit.


I don't recommend the method you used to run the Setup and Auto mode subroutines separately, because when you stop executing a subroutine, the outputs stay in their last state. It's not a huge deal in your specific program, but it's not a method I like.

Instead, I would delete the Setup subroutine and put the Auto/Setup switch and the manual pushbutton control onto a rung branch for each output in the Outputs section.

That way the Auto/Setup mode switch becomes a simple IF/ELSE decision in the Output subroutine, rather than being referenced repeatedly in the rest of the program.

Example:
Attached Images
File Type: png Output_Example.PNG (15.2 KB, 43 views)
  Reply With Quote
Old October 19th, 2018, 12:02 PM   #23
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,263
Zipped and posted: example of how I would set up the Output subroutine.

I'm still confused by the labels on the Setup/Auto switch; the label on the input itself suggests you're in AUTO mode when the input is True, but the label on the internal bit suggests the opposite.

That's one of the nice things about using an Input routine; if you have normally-closed sensors you can flip the polarity of the internal bit so that its state is more consistent with the sense of "if this boolean bit is true then this label condition is true".
Attached Files
File Type: zip LSC BIG BLUE BENDER - REWRITE2.zip (11.1 KB, 3 views)
  Reply With Quote
Old October 19th, 2018, 02:40 PM   #24
TheDude_Abides
Member
United States

TheDude_Abides is offline
 
Join Date: Sep 2018
Location: Chattanooga
Posts: 44
Quote:
Originally Posted by Ken Roach View Post
Zipped and posted: example of how I would set up the Output subroutine.

I'm still confused by the labels on the Setup/Auto switch; the label on the input itself suggests you're in AUTO mode when the input is True, but the label on the internal bit suggests the opposite.

That's one of the nice things about using an Input routine; if you have normally-closed sensors you can flip the polarity of the internal bit so that its state is more consistent with the sense of "if this boolean bit is true then this label condition is true".
I understand. I mustve updated the bit but not the input. Thanks for that, also thanks for taking the time to examine my work. Ive been plugged in most of the morning working out the bugs. It's working 99% but the operator doesnt like the point the parts rest falls so I will be finishing that out the rest of the day.
  Reply With Quote
Old October 19th, 2018, 03:51 PM   #25
TheDude_Abides
Member
United States

TheDude_Abides is offline
 
Join Date: Sep 2018
Location: Chattanooga
Posts: 44
double post
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
OT: High-Leg 240 ground fault relay. Who makes one? jdbrandt LIVE PLC Questions And Answers 3 August 9th, 2012 06:31 PM
Things you learn as an apprentice or new guy JeffKiper LIVE PLC Questions And Answers 47 May 16th, 2012 02:06 AM
GE 9030 - IMS- Powerfold sheet metal bender russrmartin LIVE PLC Questions And Answers 23 December 9th, 2011 06:07 AM


All times are GMT -5. The time now is 02:50 PM.


.