Safey issue with motors & VFDs

rdrast is correct in his assessment of the problem with the instantaneous and time delayed safety outputs.

What is being described here is referred to as a Category 1 stop as per NFPA 79 (section 9.2.2, 2002 edition). This is a controlled stop, where power is being used to control the stopping action, then having power removed after the safe stopping of the system.

I also agree with rdrast that I never put equipment in the field that does not have an isolation contactor between the drive and the motor. The only way that I would not do that is if the drive manufacturer can supply documentation indicating the drive will operate at a level of safety without the isolation contactor that satisfies your risk assessment. (Do you have one of those?)

Of course, with a 10 second wind down, I do not see a way around a solenoid locking safety switch (power to open, prefferably). The time delay output on the safety circuit is good, but a zero speed detector is better. This will be more reliable over the long haul.

Using a brake motor for this application is not the best idea from my expereince. I typically try to use brake motors for "holding" loads, not stopping them. Using them to stop the load will significantly reduce the longevity of the motor (also braking time will vary, see note above). If you are anticipating this happening only ocassionally, then it probably isn't a problem. If this is something that is going to happen more frequently, then you may need to consider the longevity of the system. Additionally, in some applications you want the motor to spin freely with the power off (like spindle applications, so that you can tram stuff). With a brake motor, this is more difficult.
 

Similar Topics

I have a German programed ME program. I want to know what tag in the PLC a latched button turns on. However when I open up the tag properties I...
Replies
14
Views
173
Hi everyone, I have an issue with installation of Studio 5000 33.00.02 DVD Media disc 2 with View Designer on Windows 11. After installation...
Replies
0
Views
67
Hi Folks, I am in the process of retrofitting MRJ2 (Mitsubishi) series with MRJ4 servo drives for two axes. I did use the conversion kit...
Replies
3
Views
77
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...
Replies
5
Views
224
Hey everyone, looking for advice in this particular scenario. Currently we have a controlnet bus that has (6) CN2DN devices and (2) powerflex...
Replies
5
Views
198
Back
Top Bottom