Hi!
My name is Marko and I have problem to setup and program S7-300; AI4/O2x8bits analog I/O module.
Please, if anyone has experience and send me an example of PLC(LAD) program that addresses and reads 1 chanal, would be great.
I am looking forward to hear from you soon.
Respectfully,
Marko.
Marko
When you insert the analog module on the rack in the hardware configuration screen it would have been assigned (or you assigned) the addresses for the analog in and out. To read the input you would just load the appropriate address (byte or word)
L IW*** (where *** is the assigned input address) or for the byte value
L IB***
To write to the output you would transfer a value to the appropriate address
T QW*** (where *** is the assigned output address) or again for the byte value
T QB***
You have not stated what analog module you are using, part number would be useful, nor what the application is.
As I have just re-read your post while typing this reply, I see that you have stated that the analog module is an 8 bit one, in which case you will use L IB*** or T QB***
I must admit though, that I have very little experience with analog module for S7's.
Hope this helps
Paul
Hi!
Thanks for the answer Paul.
I have more questions thou: How can I program the module using LEDER logic(module is: SM334; AI4/O2x8bits) and scale/unscale instructions?
The module is in slot 6(the processor accepts phisical address only) and supose to have the address PI288 PQ? .
How do I address CHANAL0?
Thanks in advance,
Respectfully,
Marko.
Analog data is written into the peripheral area of the plc, so you will have to use PIW
PIW256 is the default setting for an analog, if the address hasn't been used.
call "scale"
in:=PIW256
hi_lim:=100.00
lo_lim:=0.0
bipolar:=m100.0
ret_val=mw200
out :=LD300
Thank you Dark Knight for reminding me that I left out this important bit of information! banghead
Paul
:unsure:
Hi!
Thanks for the help!
Please, tell me how can I program the analog module using LAD logic(I am not familiar with STL).
My modul is in slot 6 (address is done automaticaly by the CPU) PI288..295; PQ288..291.
Thanks in advance,
Marko.
utoh
Hi!
Thanks everyone, you were helpful.
When I mentioned LAD I ment just I/O addresses, but you already sent me PIW 256.
My address is PIW288 for the CH0, PIW290 for the CH1...
Everything else is visible from the STL.
Thank you very much.
If there is any corection, please do it.
Thanks again,
Sincerely,
Marko.
Hello Guys! :) Good day! I am very new to S7300 Module especially Analog Modules. I am wondering if you could help me how to work with it. I have...
1,854
This is my first Siemens PLC programming. I got a PLC 315-2DP with 1 DI, 1 DO and 1 AI modules. I have already configured the modules and then...
10,574
Hello Guys, Any body has details of anlog IP wiring diagrams (S7-300, 8chn,)?
4,151
Dear experts, I would like to ask what should I configure with this Analog Input Module 6ES7 331-7KB02-0AB0. I have a 0-10V DC Analog signal...
2,949
Hello, I am using 331-7KB02-0AB0 AI 2X12 bit module. Input address are PEW 200 and PEW 202...Both are configured as 4-20mA. Now when going...
18
15,793