Delta PID controller DTA4848 c0 output signal problems
vinoddeswal
Aug 2010
delhi
hi friends,
i' m new to plc world and i was connecting a k type thermocouple to PID to get 4-20 mA output to connect it with plc analog card.but after connected i was getting values of signal output when i have achieved the set value e.g 500 deg celsius then it should show 20 mA and when temp is lower than that 500 deg then it should show lesser than 20 mA but its not varying linearly.can anyone help me out of this mess....????thankyou in advance.....
PID input is K-type thermocouple output in mV and i have used a Delta PID of current output(4-20mA)to get it connected with Omron CJ1M cpu11 plc.Please Reply its very urgent my mail id is [email protected]
Hello, it looks like you are using a standard 48x48 controller! Just remember that the controller does not need any voltage on the 4-20ma line. Just take the two wire directly to the PLC and you should be ok.
If that does not work let me know...
Cheers,
Brett
thanks for ur reply
Thanks for ur kind reply brett, but it is very late and that time i have changed that PID with Temperature Transmitter and that is directly giving me 4-20ma linear o/p as per my requirements.
Thanks again:):):):):):).....can i have ur mail id for further help..mine is [email protected]
It is possible that you tried to use the 4-20mA output as the control output. That would adapt, via PID, to various levels. If you programmed the output as a "retransmission", then it should be a linear representation of the range of the instrument. But it sounds like you are ok now, via different hardware.
Hello All I am trying to configure a delta PLC with a PID loop in order to maintain tension in a cable. The tension sensor is an AB encoder and...
1,611
Hi Everyone... Can anyone give Delta PLC PID program example.... I tried and tuned more and more.... I am not gettiing the clear idea about...
3,593
Hello dear all, Please tell me how configure the pid in delta plc please send me examples
3,225
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
90
I have downloaded COMMGR 1.15 software on my laptop. After downloading it works. When I stop and start the program again it doesn't work. It is...
145