Wrong analog input readings

Hi. OK, i have a pressure transducer for a run tank level (h20 based) that i just checked for accuracy. it's reading 3.999ma at .001in.of h20, so that's correct for an empty tank. my problem is that the way they have it wired is a signal loop................ A + and - voltage from a dc power supply is going to a PLC 5/8OE analog input card which one wire goes to the transducer to the + terminal, the transducer - terminal goes to the + analog input card on the SLC 5/04. From the SLC 5/04 analog input - terminal goes back to the pressure transducer and is wire nutted to the negative wire that goes back to the PLC 5. analog input card.The biggest question i have is that when the tank is empty the SLC 500 output the the operators panel reads 53LBS and the output from the PLC5 to another operators panel reads 285LBS. i'm thinking it must be the math functions in each of the PLC's. I have a funky little drawing for you guys to laugh at, i'm sure someone will direct me to a program i can use for creating such illustrations.
Attached Images
File Type: jpg exaple scratch.jpg (45.4 KB, 215 views)
__________________
I'm not totally lost
  Reply With Quote
Old August 2nd, 2011, 12:09 PM   #2
widelto
Member
Colombia

widelto is offline
 
widelto's Avatar
 
Join Date: Jul 2005
Location: Barranquilla, Colombia
Posts: 2,734
What is the scale from your plc5 to your transducer, and what is your scale from transducer to slc 500. What kind of transducer is that ?? Take a picture of both plcs configs. Take ( voltage/current) measurement at both input/output at the transducer when minimal value is sent from plc5. That will help you with scales.
__________________
My two cents.
  Reply With Quote
Old August 2nd, 2011, 02:05 PM   #3
TConnolly
Lifetime Supporting Member
United States

TConnolly is offline
 
TConnolly's Avatar
 
Join Date: Apr 2005
Location: Salt Lake City
Posts: 6,151
If that is a 4-20mA current loop its wired wrong at the SLC500.

From the transmitter + to the PLC5 +.
From the PLC5 - to the SLC500 +.
From the SLC500 - to the transmitter -
__________________
True craftsmanship is only one more power tool away.

That's the beauty of processors, they don't have emotions they just run code - The PLC Kid.
  Reply With Quote
Old August 2nd, 2011, 02:40 PM   #4
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,840
Wired the way it is, I am amazed it works at all.

Perhaps you could post a link to the Data Sheet/Manual for the Transducer.

This might be a good application for a 4-20mA splitter.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 2nd, 2011, 04:30 PM   #5
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,239
And also post the programs for your PLC/SLC. Tell us what modules you are using.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old August 2nd, 2011, 04:46 PM   #6
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,964
>A + and - voltage from a dc power supply is going to a PLC 5/8OE analog input card

Where's the loop power supply in the diagram?

Does either PLC provide loop power at its AI terminals? ? ?
  Reply With Quote
Old August 3rd, 2011, 12:17 PM   #7
showshocka
Member
United States

showshocka is offline
 
showshocka's Avatar
 
Join Date: Mar 2011
Location: Baltimore
Posts: 435
it's a Rosemount 1199 diapram series....the tank is not empty any more but when the tank was empty i got a reading at the transducer of 3.9ma at .001h2o level.
Attached Images
File Type: jpg PLC5shot.jpg (174.6 KB, 39 views)
File Type: jpg SLC 5_05shot.jpg (171.8 KB, 32 views)
File Type: jpg 287354_243268765693665_100000316296453_770185_2654407_o.jpg (73.4 KB, 37 views)
__________________
I'm not totally lost
  Reply With Quote
Old August 3rd, 2011, 12:24 PM   #8
showshocka
Member
United States

showshocka is offline
 
showshocka's Avatar
 
Join Date: Mar 2011
Location: Baltimore
Posts: 435
Quote:
Originally Posted by danw View Post
>A
Where's the loop power supply in the diagram?
sorry about the miss info, but the 24vdc PS is going to a strip terminal where the first connections of the PLC5 is connected to.
__________________
I'm not totally lost
  Reply With Quote
Old August 3rd, 2011, 12:40 PM   #9
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,840
Quote:
Originally Posted by showshocka View Post
it's a Rosemount 1199 diapram series....the tank is not empty any more but when the tank was empty i got a reading at the transducer of 3.9ma at .001h2o level.
Your PLC5 Screen Shot appears to be a Simulation Routine, not live Data.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 3rd, 2011, 12:41 PM   #10
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,840
Quote:
Originally Posted by showshocka View Post
sorry about the miss info, but the 24vdc PS is going to a strip terminal where the first connections of the PLC5 is connected to.
How about an updated Wiring Diagram?

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
  Reply With Quote
Old August 3rd, 2011, 12:44 PM   #11
accidentalengineer
Member
United States

accidentalengineer is offline
 
Join Date: Dec 2010
Location: Somewhere, Ohio
Posts: 53
As others have stated, it does not appear that things are wired correctly. Also some of the older PLC 5 analog in cards have dip switch settings to configure an input for either a voltage or current input as well as setting the range. And then there is some configuring that has to be done using a BTW instruction as well. It can be a pain in the !!!

Maybe the problem would be easier to conquer if you cut down in size. First concentrate on getting the transmitter to work with just the slc, then once you get that working, put the plc 5 into the loop.

Go to AB's website and get the info for each analog card. There will be examples on how to wire them for 4-20ma inputs.

Just hang in there, work through it and you will have learned a lot.
  Reply With Quote
Old August 3rd, 2011, 01:44 PM   #12
showshocka
Member
United States

showshocka is offline
 
showshocka's Avatar
 
Join Date: Mar 2011
Location: Baltimore
Posts: 435
correction, after further in investigation. this is the final wire chase. still the same the operators readouts are off PLC's are still off.
Attached Images
File Type: jpg line2 runtank.jpg (38.6 KB, 143 views)
__________________
I'm not totally lost
  Reply With Quote
Old August 3rd, 2011, 01:45 PM   #13
showshocka
Member
United States

showshocka is offline
 
showshocka's Avatar
 
Join Date: Mar 2011
Location: Baltimore
Posts: 435
Quote:
Originally Posted by sthompson View Post
Your PLC5 Screen Shot appears to be a Simulation Routine, not live Data.

Stu....
nope, that was live data as we are running now. why did you think that? the panel-view was showing 4020lbs.
__________________
I'm not totally lost

Last edited by showshocka; August 3rd, 2011 at 01:48 PM.
  Reply With Quote
Old August 3rd, 2011, 01:49 PM   #14
showshocka
Member
United States

showshocka is offline
 
showshocka's Avatar
 
Join Date: Mar 2011
Location: Baltimore
Posts: 435
Quote:
Originally Posted by sthompson View Post
How about an updated Wiring Diagram?

Stu....
done.
__________________
I'm not totally lost
  Reply With Quote
Old August 3rd, 2011, 01:53 PM   #15
sthompson
Lifetime Supporting Member + Moderator
Canada

sthompson is offline
 
sthompson's Avatar
 
Join Date: Jan 2007
Location: Vernon, BC
Posts: 1,840
Quote:
Originally Posted by showshocka View Post
nope, that was live data as we are running now. why did you think that? the panel-view was showing 4020lbs.
Because the Subroutine is called Simulation, and the Add Instruction is preceded by Simulation Timer #9, and you don't usually use an Add Instruction for Scaling an Analog Signal.

Stu....
__________________
There's never time to do it right, but there is always time to do it over!
No trees were killed in the creation of this message.
However, many electrons were terribly inconvenienced.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Chatter on output of analog input realolman LIVE PLC Questions And Answers 2 August 9th, 2010 11:48 AM
Micrologix 1400 analog input or 1762-IF4 eccan LIVE PLC Questions And Answers 2 July 26th, 2010 06:32 PM
Analog Input Wiring Question 2 kbradray LIVE PLC Questions And Answers 1 January 25th, 2008 09:11 AM
analog input simulator plc noob LIVE PLC Questions And Answers 4 December 23rd, 2007 04:47 PM
Logic Question : Tracking Parts knichols LIVE PLC Questions And Answers 26 November 16th, 2005 11:34 PM


All times are GMT -5. The time now is 01:50 AM.


.