Using RSEmulator and keep getting an error in RSLogix 5000
Forat
Aug 2015
Dubai
Hi guys, I am a total newby in PLCs, and I am currently doing a project in RSLogix 5000, using RSEmulate to Emulate the PLC, details below:
RSLogix 5000 V19.01.00 (CPR 9 SR 3)
I/O Not Responding ---> I/O OK and repeats
Under IO Configuration tree
Emualator:
Emulator RSLogix Emulate 5000 Controller Rev: 19.11
(NO FAULT)
IO module:
1756-MODULE Generic 1756 Module
(FAULT:Status: Running, Shutting Down, Offline, Faulted and repeats again.
In Connection Tab, Module Faule: Module Fault (Code 16#0203) Connection timed out.
Module Info: Module Identity Mismatched.
Backplane: a diaglog comes up saying:
"Incorrect module.
CIP object in module does not exist.
There may be a module identity mismatch or improper configuration."
RSLogix Emulate 5000 Chassis Moniter V19.01.00 (CPR 9 SR 3)
Emulator: EmuLogix5868 Controller (No errors appear on the emulator
IO Module : 1789-SIM
RSLinx Classical Professional Revision 3.51.00 CPR 9 SR 5
OS: Windows 7 Professional SP1 32 bits
I keep getting this error frequently as I open the emulator and the RSLogix program is online and it works fine, then suddenly IO not responding.
Kindly help me on this matter.
Regards,
Forat
Emualator:
(NO FAULT)
IO module:
"Incorrect module.
Regards,
Forat
All I can say is good luck!! I had to use emulate for a class I took this summer. I would spend 4 hours writing the code then 6 hours fighting emulate. All I can say is that I would shut it down, delete the simulation modules and try it again. That IO not responding was a killer though. It would work for an 1 hour then stop working all of a sudden.
I think it is crappy software.
How fast is the rpi set on your io modules? Try turning it up, from memory the default is about 10? Try 50 or so. I think this solved a similar issue for me.
That what I have been doing, it is very frustrating. RSEmulator is really bad, just a Digital IO emulator and it bearly works.
Hi Daniel, The Requested Packet Interval (RPI) is set to 50.0 ms, and still I get the mentioned fault
Why are you trying to keep the I/O module 'alive' in Emulator? Whenever I use Emulator, I inhibit all I/O modules...The tags appear and you can use all your logic, but there's no attempted backplane communication to them and therefore no errors.
I might do that, but I am keeping it alive, as to try as much as possible to recreate, an "alive plc" environment, where I get the data from the plc through the backplane of the plc, ( IO module -> Emulator -> RSLinx module ->My workstation)
But I could do that, just to check if the logic of my program.
According to RA Compatibility page, the version of RSEMulate you're using is compatible with Windows 7 Home Premium SP1 32-bit. However, there's no information about Windows 7 Pro SP1 32 bit.
Did you use the RSEMulate manual to set all the parameters in the 1756-MODULE? Did you put it on slot 3 or superior?
I think @robertmee is speaking about to inhibit "real" modules to keep their tags. You can inhibit the 1756-MODULE linked to a 1789-SIM on the emulator (or just remove it from the chassis) if you only want to test the logic.
Yeah I went to RSLogix Emualate 5000 manual page it mentions:
Windows 7 Professional (64 bits) SP1, or Windows 7 Home Premium (32 bits)
SP1, but no Windows 7 Professional (32 bits). So maybe it is the problem.
http://literature.rockwellautomation.com/idc/groups/literature/documents/gr/lgem5k-gr016_-en-p.pdf
http://www.plcdev.com/a_quick_tutorial_on_rslogix_emulator_5000
If you mean follow the steps on that page, then yes.
Well I am not working with a real module at the moment, so I am work with RSLogix Emulator, I might Inhibit the module from the Emulator Chasis as to keep the tags, without have to deal with the constant IO error.
Here's the RSLogix Emulate 5000 Getting Results Guide:
According to page 46, you need to change Input Size to 2 (1756-MODULE settings). If you followed the steps of the webpage you provided, currently you have Input Size = 1.
Try that and let us know.
No Actually I know that, There is an error in the Quick Launch Manual.
I did already put the input size to 2 (one for data and the other for fault) when I started the project.
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
33
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
63
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
75
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
155
I am trying to set up a piece of equipment with a Horner HE-X4R. I'd like to use structured text and so far I'm just trying to get a basic On/off...
64