about S7 Communication

amit.khupe

Member
Join Date
Nov 2006
Location
Mumbai
Posts
1
i want to know about S7/H400 PLC communication. which communication are available and if i wants to take that Plc on Industrial Ethernet then how to do that is this required any additional module or in processor onbord ethernet is available i m familler with AB PLC's but not able to find regarding to Simens S&/H400 plc. i have a problem that in my sys config it is shown only profibus and modbus communication so what is the distance limitation for profibus communication PLC to Engg. work station. can any one just help me out
 
Hello amit.khupe;

Both Industrial Ethernet and Profibus-DP/PA are available for S7-400H communications. For both you can use copper or fiber (not for PA of course). The limitations on the numbers of astations for profibus-DP is 31, exceptionnally.
If you want to connect through Profibus-DP to an enginnering station, you can go up to 500 m at 1,5 MB. If you need to maintain fault-tolerant connections, you will need a software called S7-redconnect on your PC to switch connections in case of communication failures.
All this information can be found (with details) in the manual S7-400_e.pdf (Automation system S7-400H Fault0tolerant System) on the Siemens support webpages.
Hope this helps,
Daniel Chartier
 

Similar Topics

We had a site where a rat gnawed through some fiber optic cables which (obviously) prevented communication to a remote rack entirely. We, and the...
Replies
3
Views
95
I have a slc500 plc 1747-L30A. Using a communication cable 1747-PIC cable box combination. Running a version of software from DOS on a Windows 3.1...
Replies
8
Views
149
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
29
Views
446
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
240
Hi all. I have a Modbus ProSoft module in my setup with a capability of 30 clients (0-29), which I'm trying to monitor the Ethernet Connection...
Replies
0
Views
51
Back
Top Bottom