Guys im troubleshooting an oil cooler unit and isolated to the power supply board for the control board.
it has a 10vac circuit going through a signal relay. i have 10vac input but have 7vac on both positive and negative at the output. im wondering if this is caused by the relay if something is going on with the traces on the board. obviously not a plc question but any help would be great thanks

Annotation 2021-03-05 173057.png
 
If you have access to the board internals then measure the voltage drop through the fuse and the relay contact.
 
several things to look at.
loose terminals
bad solder joints at the terminals, i have had that happen, look for bad solder connections/cold solder joints
fuse going bad, replace. yes, they can go bad and still work.
relay contacts are arcing and have gotten pitted, carbon deposits
james
 

Similar Topics

My one EX20 blew it's power supply board. Where can I get a new/refurbished unit in South Africa?
Replies
0
Views
1,563
I have the power supply in the link below. If we want a breaker to isolate and protect the input side how would I size that correctly being 120...
Replies
8
Views
195
I am looking for power supply that I can mount on vertical DIN rail, and when mount that way is =< 4" wide. this is what I have now.... this is...
Replies
21
Views
575
I have Rhino 120 to 24 dc power supply and it has 2 Positive and 2 negative terminals on the DC side but no ground terminal. Should I connect one...
Replies
9
Views
433
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
Replies
3
Views
231
Back
Top Bottom