ENBT/A stopped talking

TheWaterboy

Lifetime Supporting Member + Moderator
Join Date
May 2006
Location
-27.9679796,153.419016
Posts
1,924
Hi Guys

Moments ago I just had my first ENBT failure. While the front of it showed everything was fine, it would not respond to ping or to comm requests from other devices.
Configured a replacement and hot swapped it. All was fine.

Took it back to my test rack and it works fine there now. Is this a failure mode I can expect? F/W was version 6.006.
 
Look at it with Rockwells Task Monitor Tool and it can tell you if it is over loaded. I had an ENBT card that was over 80% on CPU and IO load wasn't stable. I upgraded to an EN2T card and all was well again.
 
Sometimes connections are not closed like they should be. The number of allowed connections is exceeded and it stops talking. Next time, try disable/enable from the IO tree before replacing. ( Hard to do if you cannot connect). Physically removing and putting back in place often works too.
 
Sometimes connections are not closed like they should be. The number of allowed connections is exceeded and it stops talking. Next time, try disable/enable from the IO tree before replacing. ( Hard to do if you cannot connect). Physically removing and putting back in place often works too.

It wasn't responding to anything, ping, web interface, CIP messages, nothing, so I couldn't look inside. It has been unmolested for a couple years. just picked that day to stop.


30% CPU
14 TCP Connections
9 CIP connections

32000 Conn opens (whatever that means.. connection totalizer?)
and around 30 errors or timeouts on the new one so far.
 

Similar Topics

Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
48
Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
Replies
3
Views
124
please using the usb can i assign any ip address that i want ?
Replies
4
Views
150
Hello Friends I am trying to connect to a Zebra printer. I can print the label with hyperterminal both by RS232 and TCP/IP. Now, I am trying to...
Replies
7
Views
275
Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
Replies
7
Views
1,025
Back
Top Bottom