Control net issue

kratos1

Member
Join Date
May 2017
Location
viet nam
Posts
25
Hi everyone. Please help me.
See attached picture is Rsnetwors for control net. Node 12 show: missing. I check cable connection is Ok. Control net Line A is green and in RSlogic5000 line A activated but network still fault with all devices in rack with node 12. In Rslinx also can’t find Node12.
Thanks for your support.
 
What kind of device is Node 12 ? How is its ControlNet node address configured ?

A solid green Channel A LED generally means that the device both is communicating on the network and has operating I/O connections. If there were no I/O connections active, the Channel A LED would be flashing green.

Is this an operating control system you are diagnosing, or is it a system you are starting up or modifying ?

Please post a general description of the system; screenshots only tell part of the story.
 
Thanks for your support.
Please see attached file is rsnetwors upload and PLC configuration drawing.
This is an operating system. Before Control net line A is working, Line B not active because Line B from Coal bunker not connect. After We connect , Line B still not active and Red B flashing. We found 1 issue in Rslogic5000 config 1 rack with control net module is Node 15 but in fact that this is Node 13. I don't understand why we not have fault. After that I changed this config in Rslogic from Node 15 to Node 13 and download. This rack still work, Line B still not active but Node 12 fault.
We have solid green in A channel control net module and other IO green flash blinking.I can see in Rslogic5000 CN2R_N12.Channel_A_Active but not see this rack in Rslins.When I tried to Reschedule rsnetwors. I have warning Device in Rack 12 not respond..
 

Similar Topics

Hi guys, I'm having an issue with a comms failure issue but I can't figure out the root cause. I've narrowed down the issue a good bit, and I'm...
Replies
19
Views
12,108
Hey guys, I need an urgent help. I am setting up a control net network as per attached configuration. Can you please tell me how to configure...
Replies
0
Views
2,799
Good day Forum Members I got a older Lincoln welder and hoping to make it work at our shop. Welder in question is the Lincoln Power Wave 455M...
Replies
4
Views
191
An outside contracting firm designed a machine for our company. There are several devices connected through Ethernet/IP. This includes a Panel...
Replies
4
Views
189
I am getting random comm loss (error code 561 i think?) anyway i looked it up and its loss of comm to 2 modules on a controlnet network. The 2...
Replies
0
Views
346
Back
Top Bottom