Assistance with Siemens Precharge Resistor Simovert Drive

mjaye65

Member
Join Date
May 2006
Location
Dallas texas
Posts
26
Greetings Guys,

I just finished a job where one of the things we did was replace the precharge resistors in a Siemens Inverter Drive.

In all that I know and have been taught when you replace a resistor or resistors all you have to do is match resistance value, and match or exceed Wattage rating.

In the job we just finished this prove not to be the case. There is something special about the manufacturing process of the Siemens resistor Siemens part number 6SX7010-0AC13. Description: Resistor, 2.7 Ohm, 10% Tolerance @ 110W, The MFG stamp on the resistors is R3 ZBS 30/215 2R7 10% WM110.

We did not have one of these on hand and what was supplied by our Buyers was a 3.1 Ohm instead of 2.7 Ohm, 210 Watt instead of 110 Watt, Wire wound Resistor instead of Flat wire bands with an acrylic coating encapsulating the entire resistor.

As soon as we restored power and closed the associated contactor feeding these resistors. The resistors turned into a dead short resulting in the 800 Volt contactor to weld closed. The resistors did eventually open and stop the current but the damage was done.

The purpose of the resistors is to limit current momentarily while the charging of a capacitor bank starts. Once the bank reaches 600 of the 800 VDC operating voltage another contactor closes and removes these resistors from the circuit and feed power to the capacitor bank a different way and completes the charging.

I have always received valuable information in this forum and I hope someone here as seen or used the Siemens resistors before and can tell me what is so special.

Thanks.
 
According to this datasheet the Siemens resistor is a 200 watt resistor. The WM110 isn't a power rating, it is a material of construction indicator. Also, I think the cemented ribbed construction resistors handle instantaneous peak power better than the wirewound resistors.

Keith
 
The failure was likely due to the resistor arcing thru, a peak voltage rating issue. You need the ohms and wattage and also at least 900VDC voltage withstand rating.
 
Thanks Guys,

Now cement makes sense I guess. I was trying to figure out what it was dipped or baked in and cement is what I think it closely resembles.
 

Similar Topics

I was wondering if someone here who would be much more familiar with Siemens products could answer me the following questions. What software...
Replies
1
Views
1,385
I have a Siemens program that I am unable to open due to a lack of software - we use AB and AD. Would someone be able to open the program and a...
Replies
3
Views
3,297
Hello All, One of my co-workers is trying to set up a Link 20E ProfiBus to ASi Bus gateway (Part Number 6gk1415-2aa01). I would appreciate it...
Replies
2
Views
6,057
The idea here is to provide for a brief rapid influx of message codes while preventing sequentially repeating the same message. i.e. if two...
Replies
23
Views
673
Hi All, This is my first PowerFlex 755 drive setup and I am having an issue with when I start the drive it runs at my minimum speed 5Hz, but...
Replies
10
Views
420
Back
Top Bottom