Change bit status AD P-2000

sparkie

Lifetime Supporting Member
Join Date
Nov 2014
Location
KS
Posts
1,139
I have a P-2000 and I'm trying to test out some sequencer logic. I was wondering how to change the state of a bit in a boolean array of values, but I can't seem to find out how.
 
You will have to do that in the Data View. Just create a Data View with the tags you want to force/toggle and then click on the Edit change it to a 1 and write the changes to the PLC.

If you look at the videos that are on the AD website they use this procedure a a lot during the demos.

p2000 snip.PNG
 
You will have to do that in the Data View. Just create a Data View with the tags you want to force/toggle and then click on the Edit change it to a 1 and write the changes to the PLC.

If you look at the videos that are on the AD website they use this procedure a a lot during the demos.

Thanks Bullzi. I appreciate it, I'll check their videos. One more quick question: how do you get the task number for your task. I have them named, but am not sure where the number is. I'm trying to hunt down a couple scan errors.
 

Similar Topics

Hello All. I am new to automation so please excuse my explanation. I am working on a request where I need to reset 2 alarm bits (AlarmError1_Alarm...
Replies
2
Views
1,451
studio 5000 and compact i have an int that is a 1 second increment for something when a change in the int happens regardless of up or down i...
Replies
3
Views
1,891
Hi All, I need some help on an application in which I am required to set up 30 second transition intervals between two displays. I've tried...
Replies
0
Views
1,792
This forum is full of problems that people are having and possible solutions by the guru's. But the guru's never really get a chance to 'brag' or...
Replies
53
Views
15,576
Compactlogix L33ER Studio5000 V26.01 PVP 7 standard FactoryTalk View ME V8.0 Pretty simple what I am trying to accomplish but I cant seem to make...
Replies
3
Views
5,644
Back
Top Bottom