HMI counters reset following comm error.

ziyaddin2015

Lifetime Supporting Member
Join Date
Nov 2019
Location
USA
Posts
84
Hi, All production number reset following the comm error. I've looked through logic and disabled autamatic reset future. The counters should only reset if operatore manually resets it via HMI but still resetting in the middle of a production. The machine stops for comm then counters reset when we press machine reset. We have similar lines and we dont see such issues with those lines. I have attached some pics above.

Thanks.
PLC Eaton ELC-PB14NNDR

20200221_172330.jpg
 
It is a little bit hard to understand what is happening but in that controller, only certain registers will retain their value when the controller is reset.

For number registers that you want to retain their values, registers from the range D408 to D599 should be used. If you have counters that are not in that range, they will be reset when the controller is power cycled or is reset.
 

Similar Topics

Hi I'm not skilled in RSlogix 5000.. I need to set the preset value of a counter in HMI. How can I do it? It seems that I can only write a...
Replies
1
Views
3,502
Hi I'm not skilled in RSlogix 5000.. I need to set the preset value of a counter in HMI. How can I do it? It seems that I can only write a...
Replies
1
Views
4,422
Hey everyone and anyone that can lend a helping hand. I have a project that I am being asked to add some animations of Solidworks or "3D" models...
Replies
6
Views
73
I copied a panel in factory talk HMI for an identical system. The label names are still the same as the original panel but I am trying to change...
Replies
0
Views
54
hi all i am new here i have a mitsubishi smart touch hmi i.e ms-60t-pe but i cannot find a software to edit and download a program in it any help...
Replies
3
Views
91
Back
Top Bottom