RSLogix 500 Scale Function Test

Thank you, Mickey for the further explanation.

May I know how to figure out the raw data value related with the voltage and resistor that have been chosen.

These raw data value will be the input min and max, right?
 
Thank you, Mickey for the further explanation.

May I know how you come out with the value of raw date value.
Is these the value for the input min and input max?
 
Thank you, Mickey for the further explanation.

May I know how you come out with the value of raw date value.
Is these the value for the input min and input max?

As stated above the raw data for 0-10v input for the embedded analog input for the ML1400 is 0-4095.

1.88/10=.188
.188*4095=770

9.4/10=.94
.94*4095=3849

So using the "SCP" instruction and assuming the value of your resistor is exactly 470 ohms, then

Input min=770
Input Max=3849
 
Last edited:

Similar Topics

Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
81
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
159
buen dia. tengo una falla al pasar los tags de mi plc SLC 5 0/4 a mi panel me aparece un error Problem writing value " " to item <tag name>...
Replies
1
Views
81
Will someone please convert this logic to pdf?
Replies
2
Views
127
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
Replies
1
Views
157
Back
Top Bottom