Quick question: Discrete IO does not need Block Transfer
ckchew666
Aug 2003
Malaysia
591
I'm sorry if this question has been asked before, but just want to confirm that the discrete IO does not require Block Transfer, right?
Block transfer from Flex IO to PLC5.
I don't have hardware to figure it out....anyone can throw in some feedback? Thanks.
No, Discrete I/O falls within the normal slot addressing range of PLC5 Remote I/O, so it doesn't need block transfer.
Block transfers are needed when you need to transfer more than one machine word from a slot.
Just a small correction.
With "1/2-slot" addressing, 2 words are assigned per slot.
So you can access up to 32 digital io per slot without blocktransfers.
Because of the particular addressing scheme with RIO, a degree of planning ahead is a good idea when specifying remote io modules.
For example, mixing many 8 point modules with a few 32 point modules in the same rack will be a waste of address space.
Thx for the replies.
BTW, I use one slot addressing with 32 points in Flex IO, provided i arrange them 1 Input, 1 output, 1 input, 1 output. Am i right? So, the ASB can accomodate 4 32 points module.
If I have 2 Flex IO adapter connecting to the PLC 5, can 1 Flex adapter set to 1/2 slot addressing and another set to 1 slot addressing?
Yes you can mix and match the addressing modes, but I usually recommend against it just to make troubleshooting easier.
Also, your arrangment of I/O (Input/Output/Input/Output) is exactly what is required for the 32-point and 1/2 slot addressing.
OG
OG
Correct me if I'm wrong, I taught (INPUT/OUTPUT/INPUT/OUTPUT) arrangement (32 discrete) is the arrangement for 1 slot addressing?
If we use 1/2 slot addressing we can put (INPUT/INPUT/OUTPUT/OUTPUT)? Yes? No?
Thanks.
No. On the 5's, 1 slot addressing allows for one word per slot. That is the most universal, as it allows for a complete mix and match of input and output modules. Remember, the PLC 5 series is based on R/G/S addressing. The 'R' as Rack is obvious. The 'G' part, (group) is less so; the 'S' part is the actual slot in the group (and can be 0 or 1).
I actually typed a lot here, explaining the difference, but frankly, I've forgotten, as I always use one slot mode. The PLC5 offers 1 slot, 1/2 slot, and I believe 2 slot addressing. Looking them up in the manual will define them better than what I was typing (and prevent me from looking like a fool (unless a true AB Guru like Ken, Opera, or Jesper reply )) <smile>
I know how you feel rdrast...it all kind of runs together. I almost always use 1-slot, but every once in a while the others pop up.
Here's a little summary:
2-slot
8-point any card any where (designed for this method)
16-point must alternate
32-point not allowed
1-slot
8-point any card any where (poor use of memory)
16-point any card any where (designed for this method)
32-point must alternate
1/2-slot
16-point any card any where (poor use of memory)
32-point any card any where (designed for this method)
OG
2-slot
1-slot
1/2-slot
OG
OG,
Thx for ur summary :) Now it's clearer.
My colleaque just came back from the site (PLC-5 to Flex IO installed).
The told me that the PLC-5 RIO port is linked to the Flex IO as (ASB/IA16/IA16/OA16/OB32/OB32/IB32/IB32) <-- jst ONE ASB
Does this settings means the PLC-5 & Flex IO is using 1/2 slot addressing and the it's divided into two RACK?
1/2 slot, RACK 1 = IA16/IA16/OA16/OB32
1/2 slot, Rack 2 = OB32/IB32/IB32
Pls correct me if I'm wrong, we never play around with 32 pts module before :)
Thanks.
JesperMP said:
Yes, it must be configured as 2 racks with 1/2 slot addressing.
Thx for ur confirmation, I do not know it Flex 10 ASB can be configured as 2 rack per ASB :( Too used to 16 pts Flex module with 1 slot addressing :)
Anywhere thx a lot for everyone :)
So the quick and short of the situation is that I designed an axle press that was sent to one of my company's other facilities. That facility just...
19
4,223
So I have a PID loop on an 1756-L61 running V17 software just for background. Also the PID PV is a pressure transmitter and the CV is speed sent...
893
Has anyone come across a 3 turn potentiometer that is panal mounted with either a 22 or 30 mm hole? I have been looking but nothing so far. They...
20
4,677
Hi, I am just learning CCW, finally got connected to a micro820. I'm wondering what the Version number means. The program that was already in the...
1,616
How do I measure if I am getting a signal out of the plc output? All of the outputs are giving me the same voltage, however I am certain that not...
2,166