Compact Logix I/O Not Responding
The Plc Kid
Feb 2009
Macon, Georgia
3,233
What would cause a compact logix system that appears to be running fine have a I/O not responding light on the processor display in logix 5000. This light is flashing.
I would think if there were an i/o problem that it would be a major fault and not run?
Communications can cause an I/O fault. For example, if there is a connection between setup between 2 processors and they are currently not communicating. Also, if there are VFD's on a network (Ethernet or Controlnet) and one of them is powered off you will get an I/O fault also.
We have several processors talking to each other as well as many drives.All ethernet but everthing is communicating or it would not run because of the way it is setup.
Everything is talking/running fine. That is what is bothering me so much about it. Nothing is powered off or faulted.
Get online with it and look in the I/O tree. You should see something.
If you look at the properties of your I/O cards, they have a revision that you can select. You will also see an option to select "keying". I believe that if you have it set to "exact match" and they don't match, you will get a fault. They still tend to work though. It's just a minor fault.
We set ours to "Compatible"
gents, I am trying to configure communication with EMERSON PK300 controller through port A1 using generic ethernet communication module . I could...
25
I've blown the Output Transistor on the Output Card of a Compact Logix 1769-L24ER-QBFC1B It says J378. Does anyone know the replacement part...
169
211
I was wanting to see if anyone had any information on setting up a cub5 meter and getting the data to a Allen bradley PLC. I think i have the set...
113
I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
247