alexbeatle
Member
OP
Changed the StopMode=Ramp,CF with decel=4s and the fault has gone away. Timed when the StopMode=Coast,CF it was stopping in under 1s on its own.Cables aren't shielded. I'd prefer they would be. But all of the VFD's are inside the MCP and the Ethernet are running only there - min 10cm away from the VFD power\motor cables.
Noted. Disabled since not the application and hasn't helped to solve anyways.
Will perform. Fro the Manual it only sets the A496 value. Is it safe to say that I can do it on one motor and set the same value for all of the others, since all motors are the same?
Changed the StopMode=Ramp,CF with the decel 2-4s. Will observe.