Hello all, I have a question for the experts. What I want to do is when the plc battery is low, I would like to send an alarm to my HMI panel. I am using an M221 Schneider Electric plc with Ecostruxure Machine Expert Basic software. I looked at the online manual and found this %s75 system bit, 0=normal and 1 = low battery. I am still learning plc programming and not sure how to use this system bit to write a simple ladder logic program to alarm the HMI panel. Thanks for any help.
 
One thing I forgot to mention I know how to link plc to HMI, I just not sure how to program this. When the battery is low I would use the system bit to turn on an output using a memory bit. I hope I am explaining this right.
 
Can the HMI read tags from the Schneider? If yes, then can you tell the HMI to read that %s75 bit?


If yes but the HMI cannot read the %s75 bit directly, then a adding simple rung in the PLC like this:


Code:
   %s75          a_bit_that_the_hmi_can_read
---] [---------------------( )------------------
might do the trick


If you do not understand that notation, or want to do the equivalent in ST or FBD, then you should run through the tutorial on this site or elsewhere.
 
Drbitboy is correct, however, it may be possible that the HMI you use could read that bit directly, if you are going to use an HMI or there is already one fitted then you could make this an alarm bit so it displays on the alarm banner or alarm screen, if already configured and they use a range of bits already for alarms then do as post above to map it into a variable bit. You could also create a pop or other flashing banner up on the HMI to make it a bit more visual.
One thing I would suggest is have a regular maintenance schedule to replace the batteries in all PLC's regardless of their state. We used to do this every 12 months even though some PLC's (especially if rarely turned off) may last up to 10 years. Most of the PLC's I have used you can turn the power off to replace the battery as there is normally a capacitor that will hold the backup voltage for a few minutes at least (typically 10-20 mins), however, even though some PLC manufacturers do not recommend replacing the battery while powered I used to do this and never had one loose a program.
 

Similar Topics

Dear Colleagues, I have a PLC 5/40E in one of our machine. An alarm message “PLC Battery Low” appeared at HMI. I checked the battery and...
Replies
5
Views
4,273
I'm a beginner in the automation field and I've set up an automation system connecting several devices (datalogger, radio, etc.) via Modbus RS485...
Replies
5
Views
212
Hi All, we've recently upgraded from FTView SE v10 to v12. Since the upgrade we've been having a problem where the HMI is slow to update tags in...
Replies
0
Views
87
I'm adding an IAI Gateway with 2 axes connected to it. To an ethernet network on my PLC. So, I think the math is correct on the Input and Output...
Replies
0
Views
141
Dear All, I need a sample PLC program to count the output pulse of a mass flow meter so that a specific amount of mass (for example 100gm)can be...
Replies
2
Views
146
Back
Top Bottom