Drbitboy is correct, however, it may be possible that the HMI you use could read that bit directly, if you are going to use an HMI or there is already one fitted then you could make this an alarm bit so it displays on the alarm banner or alarm screen, if already configured and they use a range of bits already for alarms then do as post above to map it into a variable bit. You could also create a pop or other flashing banner up on the HMI to make it a bit more visual.
One thing I would suggest is have a regular maintenance schedule to replace the batteries in all PLC's regardless of their state. We used to do this every 12 months even though some PLC's (especially if rarely turned off) may last up to 10 years. Most of the PLC's I have used you can turn the power off to replace the battery as there is normally a capacitor that will hold the backup voltage for a few minutes at least (typically 10-20 mins), however, even though some PLC manufacturers do not recommend replacing the battery while powered I used to do this and never had one loose a program.