Good Morning Folks.
I have a little issue with a Produced Consumed set up between an L71 V30.11 and an L33ER V30.14.
I have set this up many times over and over through our facilities using the very same 88byte UDT every time. I copy it from 1 PLC to the next.
So upon setting up both projects to look at each others PLC I noticed a connection error right away. So I went over everything, as usually its just a typo or configuration error. I deleted the processors and tags and started over, a couple times. On the L71, I get the yellow triangle on the I/O tree for the L33ER and on the L33 I/O tree I have a yellow triangle on the L71 processor but not 1756-ENBT module.
So, in further efforts. I set the controllers up to see each other without the prod/con tag. They are ok now with no errors. I can look at the properties and status of the other controller in each project and all seems ok.
Now, I went to the L71 and added 1 single produced tag of my usual UDT type. I set up the L33ER as the consumer, copy and pasted the tag straight from one project to the other, no mistake! Upon putting it all into run mode, I now see that the L71 is not showing any errors, but the L33ER has a connection error on the processor. It code #16031e Cannot Consume Tag.
(This error is suggesting that the producer tag is already at its max number of consumers as defined on its properties. However the L33 is the only consumer)
Now the odd part...... The connection comes and goes. I can change a value in my L71 on my produced tag and it will change in the L33, maybe immediately, or after a few seconds when the error clears. Then I can send more values, until the connection flashes off again with he resulting error. It dropping in and out a few times / minute.
In the L71, my Modual Definition for the L33 is set to "Disable Keying" and Connection is "None". My produced tag here I have tried to "Provide Default RPI for Consumer Out Of Range" at 10ms.
Now looking at the module definitions in the L33 for the L71 I have:::
1756-ENBT Rev4.001
"Disable Keying"
Connection is "None"
Time Sync "None"
Chassis Size is 6
In slot #3
The 1756-L71 In slot 0
Rev 30.
There are no configurable Parameters further than this!
In my L33er Advanced Properties I have clicked "Allow Consumed Tags To Use RPI Provider by Producer"
I should add, not that I think it has any bearing on the situation, that my L33ER is on the network through the NATR module. It hasn't been an issue for me as I use them on the regular with no issues before.
Any thoughts on this folks?
I'v set up this similar scenario many times and never run into this. However, normally most of my projects are Compact Logix to Compact Logix though.
Any advice would be appreciated.
Thanks
I have a little issue with a Produced Consumed set up between an L71 V30.11 and an L33ER V30.14.
I have set this up many times over and over through our facilities using the very same 88byte UDT every time. I copy it from 1 PLC to the next.
So upon setting up both projects to look at each others PLC I noticed a connection error right away. So I went over everything, as usually its just a typo or configuration error. I deleted the processors and tags and started over, a couple times. On the L71, I get the yellow triangle on the I/O tree for the L33ER and on the L33 I/O tree I have a yellow triangle on the L71 processor but not 1756-ENBT module.
So, in further efforts. I set the controllers up to see each other without the prod/con tag. They are ok now with no errors. I can look at the properties and status of the other controller in each project and all seems ok.
Now, I went to the L71 and added 1 single produced tag of my usual UDT type. I set up the L33ER as the consumer, copy and pasted the tag straight from one project to the other, no mistake! Upon putting it all into run mode, I now see that the L71 is not showing any errors, but the L33ER has a connection error on the processor. It code #16031e Cannot Consume Tag.
(This error is suggesting that the producer tag is already at its max number of consumers as defined on its properties. However the L33 is the only consumer)
Now the odd part...... The connection comes and goes. I can change a value in my L71 on my produced tag and it will change in the L33, maybe immediately, or after a few seconds when the error clears. Then I can send more values, until the connection flashes off again with he resulting error. It dropping in and out a few times / minute.
In the L71, my Modual Definition for the L33 is set to "Disable Keying" and Connection is "None". My produced tag here I have tried to "Provide Default RPI for Consumer Out Of Range" at 10ms.
Now looking at the module definitions in the L33 for the L71 I have:::
1756-ENBT Rev4.001
"Disable Keying"
Connection is "None"
Time Sync "None"
Chassis Size is 6
In slot #3
The 1756-L71 In slot 0
Rev 30.
There are no configurable Parameters further than this!
In my L33er Advanced Properties I have clicked "Allow Consumed Tags To Use RPI Provider by Producer"
I should add, not that I think it has any bearing on the situation, that my L33ER is on the network through the NATR module. It hasn't been an issue for me as I use them on the regular with no issues before.
Any thoughts on this folks?
I'v set up this similar scenario many times and never run into this. However, normally most of my projects are Compact Logix to Compact Logix though.
Any advice would be appreciated.
Thanks