I have a bX-DM1-10ED2 and i can't tell if its working or not. I wrote a simple program in domore designer that keeps the circuit on all the time and the output light stays on but i'm not sure if current is supposed to be present at the y0 (output) or not. I'm not getting any current through the multimeter.
 
Hello and welcome to the forum.

Right above Y0 you have a 1C, that needs +12vdc to +24vdc and then you should see that on Y0.

DoMore.PNG

DoMore1.PNG
 