alive15
Member
Good afternoon all, I'm looking at the PSB24-120S-3 power supply from automation direct. The recommended circuit breaker size on primary size is 16A per phase. However, the in-rush current is stated as "<30A @ 400VAC & 500VAC @ 25°C (With 3Ph AC source capability up to 3KVA) <60A @ 400VAC & 500VAC @ 25°C (With 3Ph AC source capability up to 18KVA)".
Since this power supply has the potential to have max-inrush current at 30A, shouldn't I use 30A breaker or more if I'm pulling max load on the secondary side? In this case, max Amperage will be 5A on the secondary side, so if I'm using all of that, then I would need higher breaker on primary side, correct? Looking to improve my understanding on how to correctly size the power supply on my application.
Thanks,
Since this power supply has the potential to have max-inrush current at 30A, shouldn't I use 30A breaker or more if I'm pulling max load on the secondary side? In this case, max Amperage will be 5A on the secondary side, so if I'm using all of that, then I would need higher breaker on primary side, correct? Looking to improve my understanding on how to correctly size the power supply on my application.
Thanks,