I have an application where I need to retain some data in an HMI tag. I'll explain my proposed solution, please advise if you think this will work and perhaps maybe a better way to implement it.
I have a Control Logix PLC control system (1756-L55), with lots of I/O, but of main concern are some Incremental Encoders. Part of this system are some HMIs using RSView ME (and RSView Enterprise). I am keeping track of an absolute position of a rack and pinion system using some incremental encoders (it would be nice to have absolute encoders, but the system is already constructed and its too late to change). I'm using POINT I/O 1734-IK encoder modules on ControlNet. Here's the kicker: the PLCs cannot remained powered up at all times. They must be powered down for long stretches of time (due to other factors beyond my control). Of course when they power up, they reload their program from non-volatile memory with original tag values restored. There is no way I can remember what the last count of my encoder was in a controller tag. GRRRRRRRRRR ![]() So my solution is to use an HMI tag. I have an HMI tag whose source is the controller tag with the encoder's "Current Count" value. When the PLC shuts down, the HMI tag should retain its value (I am hoping). So I write a macro in the HMI, which executes when the minor fault code from the PLC is issued which indicates a project load from non-volatile memory. The macro sets the value of the 1734-IK "Preset Value" tag to the value of the HMI tag which hopefully has the last known encoder count. Then the macro further issues commands to inhibit the 1734-IK and reset its current count value to the preset value that I just loaded. Then viola, the Current Count is the same as just before the PLC was powered down. Clear as mud? ![]() Concerns: I've never tried to set a controller tag to the value of an HMI tag with a macro before. I don't even know if that's possible. I'm also concerened that since the HMI tag is sourced by the module's "Current Count" tag, (whose value will be 0 on project load), that it will be reset to zero before my macro has a chance to write to the "Preset Value" tag. I'm also not 100% sure if an HMI tag sourced from a controller will retain its value if it loses connection to the tag server (i.e. the plc is turned off). If you understand my dilemma at all ![]() ![]() ![]() ![]() ![]() $ |
![]() |
![]() |
#2 |
Member
![]() ![]() Join Date: Jun 2002
Location: Auckland
Posts: 1,142
|
non-volatile memory on a L55?? - are you sure?
how will you know the encoder hasn't moved while power is off? get the auxiliary battery option for the processor. |
![]() |
![]() |
#3 | |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,539
|
Quote:
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen Last edited by jstolaruk; April 28th, 2006 at 07:58 PM. |
|
![]() |
![]() |
#4 |
Member
|
Go online with your PLC, put it in program mode, then open the processor properties dialog.
Under the non-volatile memory section, you can choose when the program is re-loaded. I have a machine based on Control Logix and ran into the same issue. I changed it to only load from non-volatile memory on demand. Now when the power is cycled the program is not reloaded. I learned real quick after I did a change that involved 40 rungs and it got wiped out after a brown out. Luckily I had the saved version on my laptop, but it still wiped out a bunch of relevant production data. |
![]() |
![]() |
#5 |
Member
|
![]()
Not sure if this will help but I would save a sample of the encoder readings... say 50 tags... then transfer them at a regular interval to HMI tags or some other external source. (I would use DDE Rslinx Pro with Excel. Im not sure if the tag values are retained in Rsview) After a power cycle restore the last value. ( a programmed Macro will be required here). If there is a possible movement problem, then, after a power cycle, drive the positioners to the last position value after it is restored. I am sure there are tags that retain the last value in RSview. If this is true, then after the PLC is up and running transfer the last values into the PLC tags and drive the positioner to that last known value using the encoder as a feed back for reference. Problem... sometimes this is not possible for safety reasons. Problem 2 .. The PLC isnt the contol for the prime mover driving the device. You should not have to write any special code to write values to the processor with RSview. Once Polling is restored the values should be restored to the PLC if the right tags are used. I havnt used RSview for 5 years so I could be out to lunch here. Correct me if Im wrong.. This sounds like an intersting project.. Good luck..
![]() |
![]() |
![]() |
#6 |
Lifetime Supporting Member
|
What you need to have is a homing cycle. Move the rack to a limit switch and stuff a known value in there. Require that the operator home the thing before it is allowed to operate automatically.
If you don't home an incremental axis following power up, you can't be sure the axis hasn't moved. Any other approach will leave you open to problems following power outages. These problem could simply be an axis that is "out of time" with the rest of the controls, or even safety issues and machine damage if there are no overtravel limits. I like to use an existing overtravel limit for homing and not add extra devices to the machine. JMHO Paul |
![]() |
![]() |
#7 | |
Member
![]() ![]() Join Date: Apr 2006
Location: Longview, Texas
Posts: 224
|
Thanks for the replys everyone.
Maybe I should have been more specific about the application. I am controlling leg elevating motors on a 3-leg offshore jackup oil rig to be deployed in the Persian Gulf in a few months. The encoders are on a leg motor, and basically tell me how high the rig is on its legs. Quote:
![]() ![]() Reload from EEPROM on power up is the only option. I don't want to fly out to Saudi Arabia every time they need the project loaded into the controller to reset everything. Bruce your suggestion is very good but I already have the system commissioned using RSLinx Lite. I think in my case its too late to implement a DDE solution (I have about 10 days to be up and running). I really want to do this without purchasing additional software or hardware. I want to find a solution using my current resources. I have a sinking feeling that I won't be able to retain the value in RSView ![]() ![]() Thanks again ![]() $ |
|
![]() |
![]() |
#8 | |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,539
|
Quote:
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen |
|
![]() |
![]() |
#9 | |
Member
![]() ![]() Join Date: Apr 2006
Location: Longview, Texas
Posts: 224
|
Quote:
I have given the operators the ability to reset the encoder values with the current leg depth with a very simple prodedure on the HMI. However, the customer has requested that I provide this for calibration purposes only; they want the count retained on power up. Your suggestion was one of my first suggestions to the customer as well, but they shot it down ![]() I haven't given up yet ![]() $ |
|
![]() |
![]() |
#10 |
Member
|
Ive ran into a problem close to what you have a few years back on a jack up barge. What I did to correct it loseing its place was wired the incremental encoders to remain powered all times. I also added radars(laser) on each leg as a back up.using height of deck to top of leg then sending analog ouput back to plc. I'll check around and see if I have any documentation or logic around anymore,it's been about 7 years since retrofit,and two hurricanes.
|
![]() |
![]() |
#11 | |
Lifetime Supporting Member
|
Ah...that's entirely different. Can't HOME the rig or you might drown somebody! Sounds like a perfect application for an absolute encoder. Probably not an option either right? Battery backup can be unreliable.
Quote:
Hope this helps... Another thing comes to mind: an auxilliary battery backup that should last for months unpowered. I think AB has one on the market and it should be possible to build a rechargable one. We used to use 6V motorcycle batteries on our old ISSC controllers... Last edited by OkiePC; April 29th, 2006 at 02:31 PM. |
|
![]() |
![]() |
#12 |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,539
|
Maybe a little cheesy but how about a memory card read-writer that could be communicated to via CPU's serial port? something like this:
http://www.securetech-corp.com/mcr35v2.html ![]() EDIT: actually I thought you could write with that. I was thinking along the lines of a SD or COMPACTFLASH device via RS232.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen Last edited by jstolaruk; April 29th, 2006 at 03:20 PM. |
![]() |
![]() |
#13 |
Lifetime Supporting Member
![]() ![]() Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,539
|
Actually something like this:
http://www.star.net/people/~mvs/sdrvspec.txt You've got a unique problem w/o a PC handy.
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen |
![]() |
![]() |
#14 | |
Member
![]() ![]() Join Date: Apr 2006
Location: Longview, Texas
Posts: 224
|
Quote:
|
|
![]() |
![]() |
#15 |
Member
![]() ![]() Join Date: Mar 2005
Posts: 2
|
Not sure if you still needed a work-around for this, but I had to work out something very similar to your situation. Let me know if you still need the help.
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Allen Bradley 9/260 CNC and ODS software | Graham Weaver | LIVE PLC Questions And Answers | 7 | September 27th, 2020 05:13 PM |
Learning Allen Bradley | mbferrari | LIVE PLC Questions And Answers | 9 | March 11th, 2009 01:25 PM |
Allen Bradley SLC5/04 | rsdoran | LIVE PLC Questions And Answers | 18 | January 27th, 2009 06:30 PM |
Allen Bradley PLC 5/15 | shandra_ck | LIVE PLC Questions And Answers | 16 | February 4th, 2005 10:04 AM |
Allen Bradley PLC-5 Alarming | msinclair | LIVE PLC Questions And Answers | 15 | July 26th, 2004 04:14 AM |