Hello,
I have huge problem and i hope one of You could help me. I NEED to buffer data from sensors in Compact/ControlLogix so i could send them to PanelView after process ends (entire process = 1,5h, every 5 sec 2-3 real values). Is it even doable? I cant relay on runtime PanelView data logging, because every outage or connection problem will break data transfer and valuable data will be lost. Can i store data on Compact/ControlLogix sd card and then use PanelView to read this data and corectly interpret it (so i can view this as a trend). Any help and ideas wouldbe useful.
I see two related challenges: storing the data in the controller, and displaying that data on the PanelView (Plus, I assume).
REAL tags are 32 bits, so 3 of them every 5 seconds for 5400 seconds is only 3240 records, or about 12960 bytes of data.
Array Tags in ControlLogix/CompactLogix can be up to 2 megabytes in size, so this array of about 13 kilobytes is within the memory footprint of any ControlLogix or CompactLogix controller. I don't think you necessarily need to try to write this data to the removable memory card, which is a nontrivial task: my company has spent significant time and testing developing a larger ControlLogix-based data logging mechanism.
The PanelView Plus does not have a 'chart' object.
The Trend object is always time-based. The so-called "XY Chart" does apply a separate data source for the X-axis instead of Time, but it doesn't display a range of X/Y values. Instead, it displays the Y value and X value over time.
I have experimented with "shuffling" data from an X/Y array to the XY Chart object every 1 second (about the fastest reliable way to use the Data Log Model). But it will take you 1 second per datapoint; if your "chart" is 500 pixels wide and you want full resolution, you'll wait 8 1/2 minutes to display it.
There are other visualization software packages on the market with well-developed Chart objects; in the Windows world there's a software company called Nevron with very good ActiveX products for charting.
And there are dedicated-purpose hardware products for high-reliability data logging. On-Line Development's tManager product in particular goes right into a ControlLogix chassis and can buffer significant amounts of data into an offboard SQL database.
Thank You very much! I thought there will be problem with panelview (plus compact 600). Maybe i'm trying wrong way? All i want is to make sure data from CompactLogix wont disapear no matter what (for example connection error with PanelView/PC or other kind of failures). Maybe there are other solutions that will guarantee my data will be safe and I'll be able to represent it on some kind of HMI (and later PC).
Read and write the Tags direct using pycomm3 and LogixDriver. Just in case anybody wanted to know. Here's a sample: from pycomm3 import...
808
I've recently replaced an 1756-L72 and 1756-ENBT with a 1756-L81E & 1756-ENBT2R on a ControLogix chasis. The machine ran fine for two days after...
1,693
My new friend Ron Beaufort got me thinking about the issues with using OTL's in regards to a power cycle. While you can use a first scan bit...
4,842
Hi, I'm currently putting together a schedule to bring all our compact and controllogix processors up to a standard firmware level, and then...
1,629
Ok guys so I'm trying to do some messaging between a 1756-L60M03Se Version 17 and a New compactlogix 1769-L36ERM Version 20. I tried to do some...
2,753