Help in ABB ACS550

Eslam Marwan

Member
Join Date
Jan 2015
Location
cairo
Posts
19
Hello, every body.

i need to operate a three water pump motors 4KW-3ph-380v on an one drive ACS550 4KW, i can do it by standard PFC , but the client ordered me to use also the Autochange mode.
my power circuit is to be like this

http://s12.postimg.org/y5r3gsy71/3_A.gif

but i can`t manage the control circuit, on page 189 of user manual the picture show that i need a relay logic to control of this operation.

http://www.marcopumps.gr/images/products/10-boosters/mpci/mpci-op2.jpg

I have already a Zelio logic relay (SR2B201Fu) with 12 inputs (9 digital + 3 analog) and 8 digital outputs

my question is
who can i make the autochange mode with only(ABB ACS550)if it can work

OR with
(ABB ACS550 + Zelio SR2B201Fu)

thanks for your replies.
 
Last edited:
Autochange

It appears from the manual that if you want to use autochange with ONLY the ACS550, you will have to add the ABB digital output module to the drive. Part #OREL-01 . You need 3 additional outputs for autochange. I do not have experience doing this, it is just what i can see from the manual.

CaptureABB.JPG
 
It appears from the manual that if you want to use autochange with ONLY the ACS550, you will have to add the ABB digital output module to the drive. Part #OREL-01 . You need 3 additional outputs for autochange. I do not have experience doing this, it is just what i can see from the manual.
but the OREL01 just to increase the no. of output relays. but i need a programmable logic relay to change between the magnetic contactor of each pump
 
but the OREL01 just to increase the no. of output relays. but i need a programmable logic relay to change between the magnetic contactor of each pump

I was under the impression by looking at the manual that the ACS550 has parameters to do all this. The picture show on pg#189 shows all the contactors controlled by the ACS550.
 
I was under the impression by looking at the manual that the ACS550 has parameters to do all this. The picture show on pg#189 shows all the contactors controlled by the ACS550.
on page 189 there is two picture
the left hand side show the standard PFC mode which the contactors controlled by the ACS

the right hand side show the PFC with autochange mode wich the contactors controlled by ACS and Relay logic

acs.gif


http://s10.postimg.org/8zffxqu49/acs.gif
 
Last edited:
The ACS550 already has the logic inside of it to make this happen. All you need is the expanded I/O as mentioned, and the training on the drive's internal programming to enable that functionality. Your ABB drives representative should be able to offer you instructions, or where to get the proper training.
 

Similar Topics

Good morning folks, I need your help and I am a beginner on PLC and I have been given an assignment on wiring a flowmeter to plc and create a...
Replies
3
Views
2,212
I am using a ACS800 regen drive to drive a 500hp motor for a engine dynomometer application. I am currently running the drive via ethercat...
Replies
0
Views
1,687
hi i try to do a simple program displacement program using PDispOn PROC move_up_back() PDispOn *, tool1; MoveL *, v500, z10, tool1; PDispOff...
Replies
2
Views
2,024
Hi, I want to send the data from ML1400 to ABB PLC. Can anyone help me to send the data through MSG instruction setup. Best Regards, Prasanna
Replies
1
Views
1,360
Hi i need your help , Please tell me what is the meaning of 14<<2 and other , thanks
Replies
0
Views
1,238
Back
Top Bottom