Interfacing Panelview 1000 with SLC 5/04 of Allen Bradley
ssana168
Jun 2011
Pakistan
38
Dear all,
I have one Panelview 1000 HMI and one SLC 5/04 PLC. Both are Allen Bradley. Currently my Panelview 1000 HMI malfunctioned. So i need to interface SLC 5/04 PLC with my Personal Computer. Is it possible? If yes than how.
I have saved the application file of panelview 1000 in my personal computer.
What type of network communications is implemented between the HMI and the SLC 5/04?
If DH+, you will need a Data Highway Plus network interface (1784-PKTX, 1784-PKTXD or 1784-U2DHP) installed/connected within/to your PC and one license of RSView32 Runtime (minimum 75) running the HMI's PB32 application file.
http://www.ab.com/en/epub/catalogs/12762/2181376/214372/1491278/2578666/
http://www.rockwellautomation.com/rockwellsoftware/performance/view32/orderinginfo.html
http://literature.rockwellautomation.com/idc/groups/literature/documents/um/vw32rt-um001_-en-e.pdf
If the PanelView 1000 is a "Standard PanelView" then you cannot emulate it on your PC.
If the PanelView 1000 is a 'PanelView Plus', you can run the Runtime file directly in FactoryTalk View ME (not RSView32). You will need a FactoryTalk View ME runtime license.
As mentioned above, you will also need a DH+ interface module or card for your computer; the only modern one is the 1784-U2DHP. Because there is no driver for the 1784-U2DHP in the FactoryTalk communication driver set (called RSLinx Enterprise), you will also need an RSLinx Classic OEM software license.
If the RS-232 port on the SLC-5/04 controller is available, you can use that port instead.
As I mentioned above, you need to determine if the PanelView 1000 is a "Standard" or a "Plus" unit.
The "Standard" units have a black bezel and a 2711-xxxx part number.
The "Plus" units have a gray bezel and a 2711P-xxxx part number.
Do you have the runtime file from the PanelView terminal, or the project file from either PanelBuilder32 or FactoryTalk View Studio ?
The more information you can provide, the better your Forum experience will be.
I have been trying to interface a PanelView Plus 1000 Rev 5 with a Compact GuardLogix L45S PLC. I created the screen I want the HMI to display in...
1,337
I have a task to interface Panelview 300 mono, one powerflex 40 drive and SLC 503 processor. I need to find the cheapest way to do this. Your help...
8,014
Hi, I'm kind of new to this forum and also new to programming and working with PLC's. I'm trying to develop an application at work interfacing...
7,781
I have a Cognex Insight 2000-130 camera that I'm trying to get talking to my PLC. Both are connected to the same router via Ethernet. Thus far...
1,222
Hi, I am picking up a project started by a predecessor who is now out of contact. It is a Siemens S7-1515F PLC system - but the query is how you...
726