PowerFlex 700 Comm Fault Action

rleon

Member
Join Date
Aug 2008
Location
Baires
Posts
129
Hi:

Can I make that the Comm Fault parameter (Comm Flt Action, parameter 10) of the DevieNet adapter 20-COMM-D only acts when the driver is in auto mode from MCC and not in manual mode (with the selector)?

For example, if the drive is in manual mode (with local buttons) with the MCC selector and loss communications, acts like "Hold Last", is the same to say "don't care about coms", but if in auto mode (remote) the driver acts with a stop because in remote mode I will not have the control if I loss communications.

Thanks!
 