Hell ALL,
I am having problems setting up comms between Redlion G306 and Automation Direct Click PLC.
If the drop numbers (and baud etc) are set identically in both the HMI and PLC then both the Tx and Rx on the PLC lights blink. (indicating PLC is ok?)
If the drop number assigned to the PLC slave is anything other than '0' (in the HMI comport set up as assigned to the Click) then I get CommError=2 on the HMI.
Because the numbering system on the Click starts at 1 and not 0 I can not get the lights to blink and the CommError to = 0 at the same time....???
Please Help Me!
I have successfully used a G304K2 with a Click, so it WILL work.
Here are screenshots of the settings I used. See if yours match.
-Eric
I think I just used a 3 conductor shielded cable. My G304K2 series has a different pinout than your G306, but that technote should be correct for which pins to use on the G306 end. Just don't use those communication settings.
-Eric
I'm having trouble figuring out what the actual register is to put into the HMI from the plc. Say DF1 , is it 428673? The HMI tells me that it's...
1,272
Hello ALL, I am having problems setting up comms between Redlion G07 and Automation Direct Click PLC. If the drop numbers (and baud etc) are...
3,294
Hi, I have a complex database in Crimson 3.0 and in one of the display pages I am trying to get a tag to show the sum of several other tags. The...
151
Hi All, Hoping to get some insight into best way to terminate shielded twisted pair + common into a RJ45 required for RedLion RS485...
209
I have 8 of these systems all running the same code. Just this one seem to gain about 30 seconds in time everyday. So in 48hrs time will be...
649