I'm trying to save myself some modbus mapping here...

So, can I use an existing OPC Client that talks to an Kepware OPC server to talk with a OPC UA server (Redlion Edge)?
 
The answer is that it is unlikely. It may be that your Client software ALSO supports UA in addition to DA, but it would be separate code doing each protocol.

The protocols come from the same group, but think of it like Modbus RTU and Modbus TCP coming from the same group. They're not completely different, but they aren't plug and play compatible.
 
You could use the OPC UA Client Driver in KEPServerEX to connect to a UA Server and then get the data from KEPServer with the Existing DA Client. If you are using ClientAce from Kepware and you are on V4.0 of it then you can configure it to do a UA or DA connection to a server.
 

Similar Topics

If anyone has a crack for IBH OPC Server, please send it to: [email protected] Urgently. Thanks in advance!
Replies
1
Views
53
Folks, I have a client with an old ABB Advant / MOD300 system (v14.4). Around y2k I installed the ABB Industrial IT MOD300 OPC Server 1.1/2...
Replies
0
Views
65
Hello everyone, I wanted to share my findings with getting the new OPC UA server working (I think you might be interested in this JeremyM :lolis:)...
Replies
8
Views
1,670
I have a Win10 64 bit host for my OPC DA server, which is Indusoft (Studio,Scada.OPC.3). Locally OPC works, Matrikon OPC Explorer. On my Win7...
Replies
5
Views
1,073
Hey guys, last week I posted part 1 of a series of OPC UA articles in Node-RED. That article covered some important concepts of OPC UA and how...
Replies
8
Views
3,851
Back
Top Bottom