Communication bet S7-400 and PC using NI opc server

prasad.shukre

Member
Join Date
Mar 2009
Location
surat
Posts
1
Hi All,

I am developing a SCADA for siemens S7-400( 412.2) plc. For this project i used NI opc server to build scada. My problem is that NI opc server support for serial, ethernet or modem. But siemens stopped their production for MPI serial adapter. IN NI opc server i don't have any settings to configure USB MPI adapter. How will i configure USB MPI adapter in NI opc server? Is siemens povide some drivers which support USB for NI opc Server?? Or there are another hardware (except Ethernet module)which can i use??


Prasad
 
There is CP5611 (PCI), CP5621 (PCI express) and CP5711 (USB).
They all require that you use Simatic Softnet, and not the NI OPC server. The common Siemens PC Adapter USB will not work with Simatic Softnet.

There are also 3rd party Ethernet/MPI adapters. Look for Deltalogic and IBH. I dont know if NI will work with any of these. If not, they have their own OPC servers.

Since the NI software supports ethernet, then you could add a CP443-1 to the S7-400 rack. Expensive though.
 

Similar Topics

problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,118
I'm struggling to get an FR-E800SCE to work on CC-Link IE TSN. I'm sure the issue is with the drive, when I plug in the network cable I get no...
Replies
1
Views
75
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
Replies
3
Views
95
Not sure if this is even possible but I have an micro 1400 that I would like to connect to HMI. I am using rs232 from PLC to (RS232/ttl converter)...
Replies
5
Views
213
Dear all, what type of built in port does fx2n-80mr plc has? i mean is it rs232, r rs422 or rs485. and which module should i use to convert to...
Replies
5
Views
96
Back
Top Bottom