Ultra3000i Dnet moving to preset position problems
johnfarrugia
Sep 2006
london
20
I have alomst completed a integration of a Dnet Ultra3000i servo controller but I'm having a few issues. I've attached the ultraware program from the servo controller to this thread. I am using assembly object 5 and 12 for Dnet communications. I am able to home the servo, move the servo in velocity mode as well as move the servo in indexing mode all through Dnet. Howerver, When I change the operation mode to Preset position mode, set position 0 to say...1000 counts and set start index high, nothing happens. When I disable the drive and then enable the drive it moves into the commanded position. If I home the servo while in preset position mode, it will home ok but right after it zeros, it will move to preset 0. I have tried to control the servo in preset position mode via Dnet as well as via direct I/O and they both do the same thing. I dont have "start index" assigned to any inputs I have all bits in my masked word set to 1, I'm not sure what else it could be.
Once I get the preset position mode to work correctly my plan is to store about 8 positions in the PLC. When needed, I'll send the positions to Preset 0 via the assembly object and then trigger preset 0 position.
I hope someone can help me out. I'm starting to pull my hair out!!!
Is there a reason why you want to use the Preset mode? Why not just use Indexing mode and have your PLC change the position value of index 0 via DeviceNet?
I was going to say the same thing. I have only used Indexing mode with DeviceNet or physical IO. It gives you a lot more flexibility. A few thing I noticed is that under DeviceNet, the Enable behaviour is set to 'both' but there is no physical enable input. Usually, input 1 is the enable input.
This servo is on a pick and place. There will be about 8 positions that may run in no particular order. If I use the indexing mode then I need to take the current position subtract it from the position I want to go to, figure out the difference and then send that calculated value to the servo. I can do it that way but I figured there was more code/work to using the indexing mode. I figured the Preset Position Mode would be cleaner.
Am I correct?
That's true if your motion profiles are Incremental. But if you use Absolute positioning then all the positions are referenced from the zero point. The only disadvantage is that the servo must be homed before you can do any positioning.
In the indexing panel, under mode, how is jog used? I want to allow the operator to jog the pick and place manually so I was going to place the servo into velocity mode and allow the operator to enable forward or reverse. Is this a good way to do it?
I would recommend using Indexing mode to jog your pick and place. If a motion index is set to Jog, the index will only run as long as the Start Index input is held high. Plus, it will stop if the Maximum Distance is reached. To make it jog in the opposite direction, the Maximum Distance value has to be negative. So if you want to jog both ways you have to use either two motion profiles or change the Max Dist parameter on the fly.
When I used jogging on my last project, I didn't have Devicenet so I set up two motion profiles for forward and reverse jog. The operator had a 3-position center-off momentary switch. Pushing and holding the switch either direction would set the proper motion select bits, then after a short delay set the Start Index output. It works pretty good.
Hello all, I am brand new here :cool:. I'm limited in my controls knowledge but always trying to learn more. I recently started working at a...
330
Hello, we have Ultra3000i drive(2098-DSD-HV050X-DN) with motor allen-bradley (MPL-B4540F-M) and smart encoder, indexing mode. We had defect at...
907
Hello, We have a project we are working on here at the plant. 2 AB Ultra3000i with devicenet, SLC500 5/03 with devicenet scanner. I read the...
3,727
I have an Ultra3000i Allen Bradley drive that went bad, I have a backup of the parameters and after replacing the drive I was wondering how to...
1,378
Hi, I am trying to connect to an AB 3000i servo drive through an SLC 5/04 using a 1784-U2DHP USB to DH+ converter. The servo drive is connected to...
3,844