Can't connect MP377

bakalaio

Member
Join Date
Jul 2016
Location
US
Posts
4
Hello,

I have a problem with the SIMATIC MP 377, when i try to boot i get this message

Code:
- Enabling update mode...
- Loading image from flash...
- No image found...
- Waiting for imageupdate...
i can't do nothing after that message.
I search in this forum and the Siemens support forum, and i now need to reset the panel with ProSave Software.

But i can't connect the panel with my actual configuration
There my actual configuration for connection
SIMATIC MP 377 <----- RJ45 CrossOver -----> WINDOWS PC

I don't know if i'm doing this right, but i can't find the IP to connect the panel.
There some way to find the IP using only the Ethernet between PC and Panel?

Thanks
 
You need to perform a factory reset from Prosave, which can be done via the MAC address of the MP377.
 
You need to perform a factory reset from Prosave, which can be done via the MAC address of the MP377.

When i set the ProSave to MP377, he ask for the IP for connection

and on the last tab, i need a file with extension img
some idea where i can get this file?
 
When i set the ProSave to MP377, he ask for the IP for connection

and on the last tab, i need a file with extension img
some idea where i can get this file?
The "img" file should be on the installation CD/DVD.
But.. it also installs on your hard drive when you install the software, unfortunately I don't remember the folder as I do not have a PC with the software with me.
 
The "img" file should be on the installation CD/DVD.
But.. it also installs on your hard drive when you install the software, unfortunately I don't remember the folder as I do not have a PC with the software with me.

i can use the "Backup" from another MP377?

I get this when i backup from another MP377
can i use the .img?
when i try to select this img file on ProSave, the ProSave crash.

Jjv7K2i1CqAAAAAASUVORK5CYII=
 
hi you need image files.chek the mp377 folder in win cc flexible from your pc drive
best regards
 

Similar Topics

I have a MP377 connected by ethernet to the PN-port of a CPU 319. For my connection in WinCC Flex I can select the cpu in the project, in that way...
Replies
1
Views
1,587
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
87
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
101
Here's what happened, Operator turned on the disconnect for an auger while it was still running to cut power. Auger DID in fact turn off, but the...
Replies
8
Views
335
What has been your experience with year over year price increases on your Tech-connect service contracts? Is it up to the distributor? 30% seems...
Replies
5
Views
287
Back
Top Bottom