hi,
does anyone know, are there any input modules of s7 300 plcs supporting both npn and pnp types?
at the st 70 catalog, i couldn't find any information about npn modules, how can i understand that a module is npn or pnp?
 
Under "Input Voltage" in the specs it lists what the module expects: for the SM321-1BH50-xxxx you need to offer a "low" signal for a "1", and a "high" signal for a "0". The other modules (1BH02, 1BL00, 1BH10) are the opposite. I personally don't know of any modules that do both. There is a combined I/O module, but not for NPN.
 
No.

tny said:
hi,
does anyone know, are there any input modules of s7 300 plcs supporting both npn and pnp types?
at the st 70 catalog, i couldn't find any information about npn modules, how can i understand that a module is npn or pnp?

Last time I asked Siemens I was told that the modules can either be sinking or sourcing. Cannot be configured via software to do both.
 

Similar Topics

Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
Replies
6
Views
1,361
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
661
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,040
G'day guys, I am setting up a s7-300 as a test rig for the workshop and when I downloaded the PLC is not going into run mode, I keep getting a...
Replies
35
Views
5,046
I am trying to write just MSEC to S7 300 Controller date/time using OI.SIDIRECT Aveva communication driver? The old HMI (WINCC) tag is assigned...
Replies
1
Views
1,044
Back
Top Bottom