I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.
 
I keep losing this input on an dl06 automation direct plc, all inputs are 115vac, all of the other ones are ok, just one that I have had to move twice to another input- what is the best way to protect your 115 vac inputs from failing.

What is that input coming from? Can the device you're monitoring create an inductive spike when it turns off? Can you use an interposing relay on that input?

A properly rated MOV in parallel with the input, and connected to ground may help.

-rpoet
 
Since we're talking about it, can anyone recommend a MOV or snubber they'd recommend to put across the coils?

I tried picking one out on Mouser a few weeks ago, but all the choices are overwhelming.
 

Similar Topics

Hello..I am new to Plc.I have Mitsubishi Melsec Fx3Ga-40MR PLC controlling a machine for packing powder.Currently the Plc has issue which power...
Replies
2
Views
64
Can we use a Simotion D455 ethernet port x127 as a gate, to access S7-1500 plc Tia Portal program ? In the Simatic manager, we used Netpro to do...
Replies
2
Views
71
Hi, I would like to assemble a simulator/practice booster pump system that uses PID to maintain steady water pressure under various outlet demands...
Replies
0
Views
62
I want to measure the tank level and get the sensor output to the PLC. Below are the details : Tank Height =0 - 3m, the sensor is stalled 0,2m...
Replies
14
Views
452
Back
Top Bottom