1791 DS - IB8XOB8 / A DeviceNet Safety Module Replacement
Rob S.
Sep 2008
Maryland
739
We have a DeviceNet Safety Module 1791DS-IB8XOB8/A that we need toreplace. It is faulting out from from time to time , and Rockwell Tech Support says it is the module. It seems like you cannot just change it out and go. You need to "Reset Ownership" . I don't want to make it worse and have to reconfigure the module or anything like that. What is the best way to do thiswithout making a mess. I just don't understand why it needs to be so difficult.I have the manual open and I am reading a few things about it. Any simple tips for doing this ?Thanks in advance and have a good week.
You didn't mention how the Safety Module is being controlled, but I don't know that it makes a difference. Speaking from my experience, I have a number of the 1791DS-IB8XOB8 modules on a Devicenet system with a SmartGuard 600 as the master controller. Each safety device is assigned a "safety network number." This code is stored in the device and has to jive with the code in the master controller. If I swap out a module, I have to use RSNetworx to reprogram the SmartGuard with the new safety network number for that device. It's not a big deal but does require RSNetworx software and a Devicenet adapter (1784-U2DN) to tap into the network.
It is controlled by a 1756-L61S ControlLogix 5561 Safety Controller. What happens if you just click " Reset Ownership" ?Thanks,
Check the devicenet module rev number
We had the same issue after replacing a safety devicenet module. But finally we realized new module has new revision number. So we have to goto properties on devicenet module and change the revision number to 1.3 (it was 1.2).
Make sure before you change it you have to unlock your device and go offline
Hi Everyone Have a really old line with a PLC5/30 and a lot of remote IO. Had a 1791-OA32 (32 point output module) module fail and all I have in...
3,091
We have a control system currently running a PLC5 with 4 1791 block I/O modules (16 AC inputs, 16 AC outputs) communicating over Remote I/O. The...
2,710
Hi everyone n Ken 2 :) I have a rio network setup and running. The other day I installed an additional 1791-n4c2 on the network. As we were...
1,787
I basically have a SLC 5/04 setup with 4 slots with the last slot having a 1747-SN ser.B. I have 3 other devices on the RIO link and they are...
2,709
i am planning to use this 1791 block i/o but still confused by the program addressing. can i use the same rack/group address in both input and...
1,750