1734-AENTR Input light issue
Gaurdlogix 5380 tied into 1734-AENTR. Safety scanner ossd1 and ossd2 are in I0 and I1 respectively. Common is hooked to 4&5. When we reset the scanner we get 24vdc from the scanner at the terminals of I0 and I1. But niether input shows to light up nor swap states in the program. Kinda stuck on this one. i may try to swap in a new input module and see if it works.
![]() |
![]() |
![]() |
#2 |
Lifetime Supporting Member
|
You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive. Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab. Under "Point Mode", select the Safety function for the individual input points. Usually for a light curtain or similar you will select "Safety". You also setup for Single or Dual function here with "Point Operation". Regards, George
__________________
"A little nonsense now and then is relished by the wisest men". |
![]() |
![]() |
#3 | |
Member
![]() ![]() Join Date: Oct 2018
Location: Leesville
Posts: 81
|
Quote:
|
|
![]() |
![]() |
#4 |
Lifetime Supporting Member + Moderator
|
The Input channel LED will also remain OFF if the module isn't configured yet, or if it's configured incorrectly for the inputs.
Did you inadvertently associate either of the Test Output signal sources with the inputs ? The inputs would be expecting to see the pulse train from the Test Output, not a steady 24V signal (which would indicate a short to 24V). Otherwise your wiring sounds correct for a light curtain or safety scanner connection, like the example on Page 62 of the POINT Guard I/O User Manual. edit: answered correctly while I was looking at the user manual and contemplating coffee. |
![]() |
![]() |
#5 | |
Member
![]() ![]() Join Date: Oct 2018
Location: Leesville
Posts: 81
|
Quote:
|
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Analog Input 1734 Ie2v flashing red | bornwild | LIVE PLC Questions And Answers | 2 | October 26th, 2019 12:41 AM |
RSLogix 500 - I/O mapping question | toads | LIVE PLC Questions And Answers | 8 | September 25th, 2019 12:40 PM |
FactoryTalk View SE Numeric Input Focus | zacslade | LIVE PLC Questions And Answers | 1 | March 2nd, 2016 06:26 AM |
1762-IF2OF2 Analog Input Problem | davidgay | LIVE PLC Questions And Answers | 22 | August 14th, 2013 05:25 AM |
Bit shifting? | tlvaun | LIVE PLC Questions And Answers | 17 | December 5th, 2002 11:51 PM |