Siemens S7 400 ,Allen Bradley Logix 5561 & GE Rx3i Communication

BabluRout007

Member
Join Date
Nov 2017
Location
Chealse
Posts
3
Hi Everybody ,

Please give some idea about to make communication between GE Rx3i CPU320 , Allen Bradley Logix 5581E/Logix 5561 & Siemens S7400 CPU417-4/CPU443-1 .


Thanks in advance
 
This will depend on what kind of communication you need between the units. If it involves interlocks between the processes then hardwire inputs and outputs between the PLCs. If you need communication that does not need to be deterministic then look for a protocol that is common to all of the controllers.
Modbus TCP looks to be available to all of the controllers.
https://www.rtaautomation.com/technologies/modbus-tcpip/

Hope this helps you out.
Regards,
 

Similar Topics

Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
605
Good afternoon. I need help on how to communicate the HMI KTP400 siemenes (using TIA Portal V12) with a MicroLogix 1100 Series B using RSLogix500...
Replies
0
Views
1,568
Hi, Yesterday, I was at a customer site. I made one little change. Changed a dummy bool output to an actual output. I didn't add any tags, or...
Replies
15
Views
312
Good Afternoon. I am having a problem going online with S7-400. Attached is the error that I am getting. I have looked at the help file but the...
Replies
7
Views
1,751
I can't replace cpu S400 416-3XR05-0AB0 BY 416-3ER05-0AB0 in PCS7 Project when using replace object to keep the original configuration in the...
Replies
4
Views
1,498
Back
Top Bottom