Hope someone can shed some light in to why we cant get the new nodes to be detected thru RSNETWORX.
The existing CONTROLNET has 31 nodes and is working properly w/o any issues. We are attempting to add two NEW nodes but RSNetworx is not picking-up these two new nodes. The cabling from node 31 to 32 is less than 10feet long and node 31 is the last node picked up during the scan. All the terminators are correctly done and wiring has been re-done several times in order to eliminate defective cabling. This is a redundant system (both CPU and Media). The controlnet cards on nodes 32 and 33 has flashing green OK and Channel A/B lights.
Here's what we have done sofar.
A) Added Nodes 32 and 33 I/O config in RSLogix 5000 and downloaded to Primary rack. (Redundant rack synced)
B) Physically connected Nodes 32 & 33 and powered up both racks.
C) Using Rsnetworx, scanned the CONTROLNET network. It picked up all existing nodes up to node 31, but not the newly added nodes 32 & 33. (Node 32 cabling comes directly from node 31 and 33 from 32 and 34 has terminators).
D) Manually added nodes 32 and 33 while in RSNETWORX and saved the keeper file (optimized and re-write).
E) Rescanned CONTROLNET with RSNETWORX. Nodes 32 and 33 showsup (since these were manually added to keeper file) but with a (-) minus sign next to nodes 32 and 33.
Any ideas as to what is wrong here? All the firmware rev's match on all CPU's, CONTROLNET cards, etc, etc. We are using RSNETWORX Ver. 7.0.
Hope someone can shed some light in to why we cant get the new nodes to be detected thru RSNETWORX.
The existing CONTROLNET has 31 nodes and is working properly w/o any issues. We are attempting to add two NEW nodes but RSNetworx is not picking-up these two new nodes. The cabling from node 31 to 32 is less than 10feet long and node 31 is the last node picked up during the scan. All the terminators are correctly done and wiring has been re-done several times in order to eliminate defective cabling. This is a redundant system (both CPU and Media). The controlnet cards on nodes 32 and 33 has flashing green OK and Channel A/B lights.
Here's what we have done sofar.
A) Added Nodes 32 and 33 I/O config in RSLogix 5000 and downloaded to Primary rack. (Redundant rack synced)
B) Physically connected Nodes 32 & 33 and powered up both racks.
C) Using Rsnetworx, scanned the CONTROLNET network. It picked up all existing nodes up to node 31, but not the newly added nodes 32 & 33. (Node 32 cabling comes directly from node 31 and 33 from 32 and 34 has terminators).
D) Manually added nodes 32 and 33 while in RSNETWORX and saved the keeper file (optimized and re-write).
E) Rescanned CONTROLNET with RSNETWORX. Nodes 32 and 33 showsup (since these were manually added to keeper file) but with a (-) minus sign next to nodes 32 and 33.
Any ideas as to what is wrong here? All the firmware rev's match on all CPU's, CONTROLNET cards, etc, etc. We are using RSNETWORX Ver. 7.0.