Dear Experts,

Is it allowed to use 4 wire sensor 4-20 ma (external power loop) with
control logix analog card ( 1756-IF16 )with a single ended current wiring
Because in manual they put only 2 wire sensor (attached)

Thanks

ff.PNG
 
If there is a potential difference between the power supply ground in the field device and the (-) return on the AI, then the signal will have an 'offset' created by a ground loop caused by the difference in ground potentials. The offset will affect all the AI's, not just the one causing the ground loop.

This happens quite commonly with single ended AI's. If it happens, then you need a signal isolator (4-20mA input/4-20mA output) to get rid of the ground loop.
 
If there is a potential difference between the power supply ground in the field device and the (-) return on the AI, then the signal will have an 'offset' created by a ground loop caused by the difference in ground potentials. The offset will affect all the AI's, not just the one causing the ground loop.

This happens quite commonly with single ended AI's. If it happens, then you need a signal isolator (4-20mA input/4-20mA output) to get rid of the ground loop.
Thanks Danw for your comment, yes this happened with me before that all instruments connected to PLC their readings well and stable and when I connect specific instrument all instrument readings giving me wrong readings.
But what is the main reason of potential difference between the two (-ve) and how I can eliminate this??
 
There are engineering design guide books written on the topic of control system grounding.

The bottom line is, it's too time-intensive and costly for people at the controls end or integration end to re-engineer plants to minimize ground loops. The practical solution is to use a signal isolator.
 

Similar Topics

Hello, I am attempting to wire instrumentation to an AB IF16 analog input card. In examining the documentation for the card, I've come to know...
Replies
1
Views
7,169
I am trying to spec out some PLC modules for an upcoming project. Our vendor suggested we use a 1756-IF16 analog input module for connecting to...
Replies
2
Views
7,439
https://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um009_-en-p.pdf In the above 1756-IF16 document on page 43, it...
Replies
8
Views
4,966
I actually don't understand which device determines whether the wiring will be single ended vs differential. being single ended or differential...
Replies
4
Views
3,144
Hello, I have a 1756-IF16 configured for single-ended current inputs. I plan to add (4) 4-wire density transmitters. The operating manual for...
Replies
3
Views
2,338
Back
Top Bottom