Phoenix Contact ILC171 to Siemens CU320 Profibus communication issue
Roborooter
Jan 2015
Vancouver
Hey All,
I am trying to get a Phoenix Contact ILC171 to communicate with a Siemens CU320 via a profibus module (IB IL PB MA-Pac). I currently have the Phoenix Contact PLC reading from the Siemens controller but the Siemens controller will not accept anything from the Phoenix Contact PLC. I was able to get in contact with Siemens and they said that I need to make sure that Bit 10 of the fist word of each object is set to true. I was under the impression that the telegrams that Siemens uses would handle the framing.
I am currently using Siemens telegram 105, PZD-10/10: SIMAMICS S DXB_PB in PCWORX and Free telegram configuration with BICO with Input data length 10 and output data length 10. There does not seem to be much more configuration I can do unless I am missing something. The pictures included are of the configuration in Siemens STARTER and Phoenix Contact PCWORX.
Any help letting me know either what you think is wrong or how to try what Siemens suggested would be very helpful.
PCWORX_Bus_Configuration.jpg PCWORX_I-O_Configuration.jpg STARTER_Profibus_Recieve_Configuration.jpg STARTER_Telegram_Configuration.jpg
Robo
What made you decide on Telegram 105? This is designed for Simotion and T CPU where DSC (dynamic servo control) is used
I cant see Phoenix implementing this.
What is your application? point to point moves? or?
Hello JRW
I am using the CU320 to control VFD's which are connected to generators. So I have continuous movement with torque/speed control.
As for choosing Telegram 105, I figured the framing would work regardless of telegram and telegram 105 has 10 words in and 10 words out, which is what I need for data logging. I guess I will have to do some reading into Siemens telegrams.
Thanks for the reply.
I am stuck on fail ctrl error 1013 cannot get IP nor can do firmware update need help pls urgent
170
Hi, I'm working with a Phoenix Contact FL NAT 2304-2GC-2SFP Ethernet switch, I already set the IP address and it has been working fine. I can...
1,267
Hi all, Historically i have used AB compactlogix exclusively working within the Logix/Studio5000 environment. I have decided to step out of my...
1,880
Hi all, first time poster and working on an existing PC TriSafe PLC for the first time for a project. I am wondering if anyone would know if...
1,109
(Rant)(CAD Models): Phoenix Contact Took the Time to say "FU!!" to their customers So obviously they have real CAD models of their parts because...
1,757