SLC5/04 to Mettler Toledo comms

ezetric

Member
Join Date
Jul 2020
Location
Nashville
Posts
1
I have an existing machine with a SLC5/04 processor. It communicates to a Mettler Toledo IND780 scale controller via remote I/O and a 1747-SN scanner module in slot 1.
The machine has worked for years and suddenly lost comms from the scale to PLC. The DH+ cable is daisy chained from the 1747-SN to the scale controller, then to another rack with a scanner module elsewhere with terminating resistors at the ends. The other rack is communicating so I assume the cable is good. The cable also reads good with a meter. The original scale controller was obsolete so I had it replaced with a new one with the RIO board. It still doesn't communicate.
I think maybe there was a power outage and the original controller lost its parameters. I don't have these parameters documented anywhere so I'm not sure what the settings should be. The scale does work and we are able operate manually but very slowly. The scale is used to make chemical blends. The comms light on the PLC blinks green slow.
Here are the scale RIOparameters:
Node address (this was called rack number in the old controller)
Start Quarter (choice of 1-4)
Last Rack (yes or no)
Data rate: 19K 56k, 230k (DIP switches on 1747-SN are set to 230k)
Block Transfer (enabled or disabled)
Data format: Integer, float, etc.
Byte Order: Word swap, byte swap, or historical
In the PLC, the Inputs start at I:1.16 so I assume the node is 1, but I have tried 1-4. I have also tried start quarter 1-4, still no comms.
I attached a file showing some setup tips when going to a newer version of the scale and another file from the rung comments in the PLC. I also attached a screenshot of the 1747-SN settings.
Any info would be appreciated.
Semper Fi!

EA Blend Scanner Module.png
 

Attachments

  • EA Blend Scale Mettler Toledo JagXtreme Info From PLC Rung Comments.docx
    15.1 KB · Views: 4
  • Mettler Toledo Jag_RIO_Replacement.pdf
    213.9 KB · Views: 5
Last edited:
Welcome to the forum. Maybe this will help figure out your old scale parameters. We have an old Jaguar terminal running two platform scales, RIO to a SLC5/05. Pics of the terminal are to identify what we have. The notes are what the operators use to re-enter the parameters after a power cycle.

I’ll be at the plant tomorrow if there’s anything in particular I could check for you. The system will soon be replaced with ControlLogix and two Ethernet I/P terminals.

8EB55C24-BCCD-4C03-8205-CA905733D5B5.jpeg 4E5D8617-8F14-41C7-B2A7-4034C3B9E27F.jpeg BBC3AA5A-27C6-4A73-BCD0-E7D3F086B158.jpg
 
Hey, I have been browsing forums looking for a solution. I am having the exact same issue. I have the same scale/processor/comm. card. Did you ever resolve the problem you were having?
 

Similar Topics

I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,543
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,258
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
Replies
3
Views
624
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
911
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
Replies
3
Views
976
Back
Top Bottom