Powereflex 525 Programming
Zubisafdar
Aug 2020
Canada
Hi Everyone,
I have a project where I am controlling the speed of my 3hp pump using powerflex525 with the pressure sensor PA3224 that is 4-20mA. I am having difficulty with the setting up the parameter for PID loop to control the pump speed where if it sees the 4mA it will run faster to send more product and at 20mA the pump slower down to just maintain the setpoint.
I have set the following parameter
p047 is set to 11
A459 is set to 0
A460 is set to 1
A464 is set to 40
my pump conitunouly running even after 40 and not reach to the limit where it should stop. I am using even parameter
t100 is set to 0
t101 is set to 25
t102 is set to 50
t103 is set to 60
any help appreciated to control the system.
From the manual-
t100 [Sleep-Wake Sel] Related Parameter(s): t101, t102, t103
Drive “sleeps” if the appropriate analog input drops below the set t101 [Sleep Level] for the time set in t102 [Sleep Time] and the drive is running. When entering sleep mode the drive
ramps to zero and the run indicator on the keypad display flashes to indicate the drive is in “sleep” mode.
When the appropriate analog input rises above the set [Wake Level], the drive “wakes” and ramps to the commanded frequency.
Inversion can be accomplished by setting [Sleep Level] to a higher setting than t103 [Wake Level].
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
230
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
241
New to vfds. I put in parameters. IP, but I get ethernet flashing and link solid. What did I do wrong?
473
Are the N files in the 525 the same as the 40p for ethernet? (E-Comm card) I have used 40P with Micrologix 1400 Messaging but don't see the N...
226
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
296