I have been working on more and more systems with E300 electronic overloads as a requirement.

I know ENET technology has come a long way, but as a safety reservation, i have always allowed a Physical PLC Output as an Enabel for each starter.

I was wondering what others take on this is or how have you addressed this. There is system ESTOP obviously, but this is something i have always done.

Would appreciate some feedback.
 
Physical PLC output could fail just as easily as a command over ENET and the Physical output is actually more likely to fail of the two.

Your safety system should be the area of concern and make sure it's up to the task to catch any equipment failures and put the system in a safe state.
 
Never used one. Is the big selling point an ability to remotely monitor current and reset if it trips, or is there more to it? And you still need a DO to fire the starter, right?

A quick price check from our vendor shows that contactor+E300 overload is very close to an ENet VFD.
 
Last edited:
Physical PLC output could fail just as easily as a command over ENET and the Physical output is actually more likely to fail of the two.

Your safety system should be the area of concern and make sure it's up to the task to catch any equipment failures and put the system in a safe state.

Maybe i wasn't clear in my system, but its not a safety system, but the ability to shut it off if something goes sideways. When i talk about fail, i mean fail closed to prevent the ability to stop it.

Never used one. Is the big selling point an ability to remotely monitor current and reset if it trips, or is there more to it? And you still need a DO to fire the starter, right?

A quick price check from our vendor shows that contactor+E300 overload is very close to an ENet VFD.

The E300 can be used to monitor the amps and start/stop the motor along with monitor all status. You don't need any physical inputs/outputs depending on how you configure it.

Not sure what VFD you are comparing it to, but the costs shouldn't be that much. It is sure an extra ~60% of the starter cost, but eliminated field wiring and PLC IO.
 
So in your scheme of always using a PLC Output to enable a starter “as a safety reservation”, is that hard output required to be only in the main rack with the CPU? If not, then what’s the difference between a network enabled smart OL relay as the control device and a network enabled remote PLC I/O rack or device?
 
Last edited:
So in your scheme of always using a PLC Output to enable a starter “as a safety reservation”, is that hard output required to be only in the main rack with the CPU? If not, then what’s the difference between a network enabled smart OL relay as the control device and a network enabled remote PLC I/O rack or device?

Good point. Though probably a lot more tedious to supply each E300 with MCR power or break its signal to the starter vs. using a multi-channel DO card. And doing so kind of eliminates most of the wiring advantage of the E300, no?
 
Last edited:

Similar Topics

Hi, I'm using E300 as E3 Plus in emulation mode. E300 is Rockwell Automation's overload relay. But I get hardware fault when I enable Ground...
Replies
0
Views
413
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
Replies
8
Views
961
Hi everyone, I have So many E300 Control module kept dead due to Module status fault. I am trying to flash them to higher version from lower...
Replies
0
Views
374
Hello, How do I go about adding an e300 to a motor greater than 200A. I have no problem adding it to any other motor less than that. Thanks!
Replies
2
Views
1,073
Hello everyone. I have a bunch of e300s connected to a startix which is then going to the plc. All of them are showing their MS and NS lights...
Replies
12
Views
4,297
Back
Top Bottom