carlo gavazzi setup
hello ByteCruncher,
I hope i can still help.
what I did is i didn't use any EDS anymore.
for some reason its not working.
I manually did it using Messaging.
If you can ping your Power Meters on the network that would be good.
next thing you download this file and you can see here the addresses of the data that you want to see in your scada.
https://www.enika.cz/data/files/produkty/energy%20m/CP/WM30-WM40%20CP-EtherNet_IP%20V1.1%2021052015.pdf
1st ping your PM if the network can see it.
check the pdf go to page 14. (this is just an example)
giving you an ex of the instantaneous variables (voltage and current)
notice that the CIP Assy. Inst 101d.
that is the address that you will use in messaging
and I created a tag which is real and has [12] arrays.
2nd setup your Messaging
you message type is CIP generic
service type is get attribute single
automatically Service code will be e.
class would be 4 and attribute is 3. (i forgot the reason why i use this digits.)
now the instance is the group name you will input there 101 instead of 101d.
destination is the variable where you going to put the read data.
ex. VolandCur[0] (i created 12 of this so its from 0 to 11).
you will use the VolandCur[0] so that it will start there.
3rd communication getting the path.
if your using an AEN2TR OR ENBT anything actually.
what you should do is use the name of the Enet device.
ex if you named it Gateway use Gateway, 2, (ip address)
4th tag.
just the name of the Messaging.
if that doesnt have an error go to your tags and then go to your destination tag and you will notice its reading data now.
i very hope this will help you.
its been too long.