Advantech AS4000-CR60 HMI upload

technolog

Lifetime Supporting Member
Join Date
May 2015
Location
Ohio
Posts
316
I have an Advantech AS4000-CR60 HMI that I need to get an upload from. Is the software still available to allow me to do this? Does anyone know where I can obtain a copy? Also, if necessary, do you know of the cable part number required for the upload or pinout details? I say "if necessary" as it has an RJ45 port which I'm assuming is Ethernet.
 
It was a rebranded Indusoft Web Studio version, running on Windows CE (5 probably).
You can plug a USB drive (formatted FAT) into the HMI, use the CE desktop's Windows Explorer to copy the .APP (and adjacent directories, all of them) from the \HARDDISK to the USB stick.
 
I can't exit the HMI application to get to the WinCE desktop. Is there a procedure to do this?
 
ALT+F4 didn't work. I tried CTRL+ALT+DEL and CTRL+ESC too.

When it boots, the CE desktop is visible but it auto loads the application and I can't figure out how to stop it. Any ideas?
 
While it's booting and showing the first logo try F2, F8 or F12 to see if you get to BIOS setup or a boot menu.

F12 is usually a boot menu, F2 goes to BIOS. Some computers respond to F8 or Delete to get to menus or setup.

Also, if it's a touchscreen there usually is a corner combination to hold while booting that gets to a menu instead of starting the application.

Also, I have seen where a menu pops up instead of starting the application if a USB drive is in when booting. That one was Chinese.
 
In the extremely distant past there used to be a key combo to cancel all 'startup' items. I have no idea if it applied to WinCE, it was more of a Win3.11, Win95/98 thing (I think I even used it on Win2k/XP).

From the moment the computer is powered on throughout the entire boot sequence until the desktop is well loaded, hold down both the Left And Right Shift keys together.
 

Similar Topics

Hi, I have an older Kohler Generator/ATS controller that has a Schneider Electric (Modicon) Momentum PLC and has a Advantech HMI. I assume this...
Replies
3
Views
693
German and English Grüß euch, ich hab im Forum zum Thema Panel download leider keinen Beitrag gefunden und möchte euch folgendes fragen: Ich...
Replies
5
Views
1,095
I am trying to read Schneider power meter PM2120 data using M221 plc.Power meter Pm2120 is connected to serial port of modbus/tcp gateway...
Replies
0
Views
1,516
Hi Team, I am looking at spec'ing an Advantech Industrial Managed Ethernet Switch in the design of our OEM equipment to talk EtherNetIP to the...
Replies
0
Views
1,659
I need help setting up Modbus RS485 communications between a Red lion G307K200 and an Advantech Adam 4168 to both read and or force the output...
Replies
5
Views
3,906
Back
Top Bottom